3-phase Design Quandry
#51Posted 2009-10-30 08:23:59
One was looking at reducing the MD and the actual load for economic reasons and also have you considered the effect of all this loading on other consumers fed from the transformer?
An instantaneous HW unit(s) and a hotplate unit with perhaps two A/C units running? The HW may be on for 5 mins but that is all extra load on the supply authority system. In Qld, Australia, instantaneous HW units are not installed in residential instalations. HWS are storage systems generally 45L to 270L with elements from 1.8 to 3.6kw. They can be connected on "off peak" tariffs, depending on their watts/litre rating and switched on and off as required by the supply authority though a relay on the customers main switchboard. There was an instantaneous shower heater available over 25 years ago that consisted of a shower head with a 10 A or 15A element, one had to turn the water on first then the power. and they were very prone to burn out due to the fact that persons using the shower would turn off the water but forget to turn off the power. They went off the market in the end as HWS became cheaper. It is policy to promote solar HWS ( with booster element available) in all new domestic installations now. Instantaneous water heater systems are available but are used for commercial and industrial applications. Not in a domestic environment. On the subject of socket outlets 20 twin x 10amp is ample for the average residence, runover 3 circuits two running through the "kitchen area" Electric hotplate units, these could be replaced with LPG, thus reducing the MD. We have to look at using energy more efficiently in the future and that means using load management combined with off peak use with favourable tarriffs. But I am impressed with the shower heaters now available in Thailand but they do need good water pressure for them to work properly ie. the 10 A models only. But I would doubt if they would meet the current approvals standards in Australia, they are well priced however. Generally HWS are set to 70C and the smaller units for dishwashing etc are set to 82C. #52Posted 2009-10-30 08:47:32
Just as a matter of interest do you know the size of your distribution transformer in KVA? Do you know the existing number of consumers fed from this distribution transformer at present?
#53Posted 2009-10-30 16:51:37
if you are interested we have a second hand surface mounting Square D load center, its a 30 pole 100 A max here is the cat number QO3-100EZ30G/S it is fitted with a EZD100H 60A main breaker all in very very nice condition Now I know that these things dont come cheap so this might be a way to save a few notes. let me know if you are interested Hi Bangkok, Thank you for your kind offer, and PM. Regrettably, my order has already been placed for everything, and it is scheduled for delivery. I would be interested to know though, (and hope Thanks again. ~~z #54Posted 2009-10-30 17:38:38
Hi David96,
You make some good points. Unfortunately, the construction is already about 80% complete, including the wiring, so I am not at liberty to change very much. This whole thing has been a pretty stressful experience, and if I had the opportunity to do it over again there are a number of things that I would do differently. But right now, my goal is to get it over with, with as few more modifications to the design as possible. Regarding the number of GPOs; you, (and Elk), are right -- I probably overdid it. But I've been in so many Thai houses that had too few GPOs, and then tripped over writhing octopuses of power strips, getting from one side of the room to the opposite. And also there are too many lights in the design. Many of these lights and GPOs will probably get very little use, but I suspect that they drove Elk's MD calculations up measureably. Re your following questions:
Just as a matter of interest do you know the size of your distribution transformer in KVA? Do you know the existing number of consumers fed from this distribution transformer at present? Sorry, I don't know either. And neither did the PEA chap. He will have to do his "survey" to determine what will be necessary to extend 3-phase to the property. What I do know is that he quoted 38,754 THB for a (30/100) 3-phase meter, but only 12,383 THB for a single-phase (30/100) meter. #55Posted 2009-10-31 06:11:35
It will be interesting to see what your actual load will be when your electrical installation is finally connected to supply, it should be well below the calculated MD.
That cost for energy metering would include meter and connection to supply, single phase or three phase. Meters remains the property of the PEA. Strange that the PEA does not know the size in KVA of the distribution transformer it is usually stamped on the side of the transformer and can be read from the ground. 50KVA and 100KVA are common sizes for distribution transformers. It is obvious that from your MD you may have to go to a 3 phase supply. Otherwise it is 22kw all on one phase or balance 22kw over 3 phases. ie approx 7kw per phase. And if the PEA transformer is found to be too small it would have to be upgraded. #56Posted 2009-10-31 07:56:48
It will be interesting to see what your actual load will be when your electrical installation is finally connected to supply I asked my ET why I couldn't just buy the two meters and have him install them. He said that there would be more to it than that, that there would be additional electronics involved that he wasn't qualified to take on. (He, IMHO, is a good electrician, but he is (self-confessed) not an electrical engineer.) Any thoughts? #57Posted 2009-10-31 09:16:38
I have been thinking the same thing. In several locations around here I have seen voltmeters and ammeters side-by-side in a panel next to the load center. This would seem to me to be a practical way to monitor actual consumption and voltage drops as they occur. I asked the Schneider/Square D folks if they sell such units. They don't. Do you or anyone else know if there is a standalone box that will do this, or does it have to be specially built? I believe ABB have them but I suppose they are for DIN-rail mounting. Look at the their catalogue for the pro M compact series (Jan 2009) (pdf) here: http://www.abb.co.th...q=pro M compact #58Posted 2009-10-31 09:49:43
I have a second hand one here, it is designed for three phase, you can switch the meters to different phases to view the volts and amps. it also has three lights that show that the three phases are working.
it has been set up to take a 30 pole Square D load center in it. I will take a pic and post it soon for you, and your sparky is right there is some extra wiring in there that allows for the switching and loads. will post pics of that too for you #59Posted 2009-10-31 11:05:44 ![]() ![]() here are the pics of the cabinate and the meters, if you are interested in buying second hand then give me a PM #60Posted 2009-10-31 20:41:19
I believe ABB have them but I suppose they are for DIN-rail mounting. Look at the their catalogue for the pro M compact series (Jan 2009) (pdf) here: http://www.abb.co.th...q=pro M compact
I have a second hand one here, it is designed for three phase, your sparky is right there is some extra wiring in there that allows for the switching and loads. will post pics of that too for you
here are the pics of the cabinate and the meters, if you are interested in buying second hand then give me a PM Thank you bangkok. I may be interested. However this stuff is all new territory for me. I'm trying to get my head around all of it. I presume the center picture is the back of the first picture. But the right-hand picture -- what is it's function and where is it located? And what are all of the dimensions? But secondly -- the obvious question, presuming that it all works well, why are you not using it? #61Posted 2009-10-31 20:51:45
ok the center pic is of the open door it is the back of the meters.
the right hand pic is the inside of the cabinate behind the meters, the blue units are the coils for measuring the amps, the mains wires go through these coils. this is just some of the things we have in stock about the place, it is interesting what you collect over time, we have quite a lot of three phase stuff about. #62Posted 2009-11-03 00:12:44
Hi Zap.
You will not really save anything if you worry about socket outlets. Even if you halve the current of them, you will still end up with about 80 amps for your MD (27 amps per phase if you have 3 phase). You may save a little bit in the cable cost. Let me reiterate the socket outlet part of the MD calc: Upstairs <60 = 25 amps. Downstairs <40 = 20 amps. Under your circumstances, this seems to be quite resonable given that each socket outlet is rated at 10 amps. Your "after diversity calculation" arrived at a total of 45 amps for <120 socket outlets. The method used to calculate your MD is one of 4 methods available (yours was "calculation"). The other methods are: 1] Assessment. 2] Measurement. 3] Limitation. Assessment is the most difficult to do...especially in a domestic situation because people tend to change their habits etc. Also, when new family members arrive (babies etc), this causes yet another change. Measurement is possible but it will only be of any use if the current used is monitored over a long period (months or better yet, 1 year). The limitation method is simple but very expensive...even more expensive than your current calculation. From the Standard; Quote Where more than one item of equipment is connected, the circuit current could be simply assessed as the sum of the individual equipment load currents. While this would provide a safe and conservative solution, it does not take account of the normal operating conditions during which all equipment is not operating simultaneously at full load or for long periods, e.g. submains to a distribution board associated with numerous socket outlet circuits. Under such conditions the circuit current is estimated using diversity factors and is often described as the 'after diversity maximum demand'. The diversity factors applicable to any given circuit in an installation will depend on a number of features of the installation including— [a] conditions under which the installation is expected to be used, e.g. residential compared with commercial; and [b] operating characteristics of the connected load, e.g. airconditioning load in tropical locations compared with heating loads in cold-climate regions; and [c] number and physical distribution of points provided on the circuit, e.g. socket-outlets provided for convenient connection of portable equipment compared to dedicated or fixed equipment loads; and [d] size and type of significant loads, e.g. large motors or industrial plant. It should be recognized that the determination of diversity factors is not accurate for every installation and different installations of the same type may have significantly different load profiles which the designer needs to consider. The methods provided herein have been used over several editions of AS/NZS 3000 and, provided that care is taken to assess the presence of unusual equipment loads, are considered appropriate for many typical applications. When the load is assessed and the current-carrying capacity of the circuit is determined by allowing for diversity of operation of equipment, then the circuit should be protected by a circuit-breaker of rating to comply with Paragraph B3.2. If you wish to gamble, that's up to you. When it comes to electrical, I trust a tried & tested standard. The 5 cents you might save today may cost you a lot more in the future. BTW, electricians in Australia would end up with the same result as I did. The "not so smart" electricians tend to gamble (which means "guessing"). They do this to "win the job". Two important purposes of using "After Diversity Maximum Demand" are to avoid FUTURE situations of voltage drop & hot cables (fire). If you have the notion of installing voltmeters & ammeters, it is not as easy as you think. For a start, you will need a much larger switchboard. Then, "cutouts" will need to be made for the meters & rotary switches. BS88 (or BS1361) fuses will need to be installed for fault protection. There are no electronics involved but there is control wiring. I think you have nothing to worry about. You have a valid MD calculation that has been tried, tested & otherwise proven to be safe & unproblematic. I think you really need to concentrate on what the PEA are going to do about your MD, whether you take a short cut & make it 80 amps or use the present MD of 100 amps. You need to make sure that they will use the correct cable for your installation. Also, don't get caught up in a battle with them (PEA) about paying money for transformers. Far too many foreigners fall for this trick. If you are in a "zoned" area for building, you need to find out what the electrical limitations are for your zone. I'll bet it's not a 15 amp meter! The PEA must supply you with electricity at their cost (if you are permitted to have a large supply). The exception is if you live a long way from power lines, in which case, you will pay for cable & transformer costs. FYI, typical transformer sizes in Thailand are from 20KVA for an individual installation to about 250KVA for local distribution. Edited by elkangorito, 2009-11-03 00:14:48. #63Posted 2009-11-04 09:27:52
Hi Elk,
Regarding your below, let me assure you that I don't intend to try to "cut corners" here by presuming a lesser MD than you have calculated. I have already exhausted my questions regarding the possibility of reducing the MD, and you have addressed them satisfactorily. The switchgear that I have already ordered complies with your MD. (From memory..., I think your arithmetic was): MD = 101amps, 101/3 = 34amps/phase, +20% for expansion = 40amps/phase, rounded up for conservatism = 50amps/phase. The switchgear that I have ordered complies with that 50amps/phase, and is consistent with our emails and posts. In short, rather than gambling (your correctly chosen word) with a lesser MD, I prefer to be cautious and conservative. And indeed, I wish to use the appropriate main supply cable. But that's where the present confusion lies. I'll get to that in the next post. Here I would just like to say that your extended discussion of the MD calculation makes this topic much clearer. Thank you.
Hi Zap. You will not really save anything if you worry about socket outlets. Even if you halve the current of them, you will still end up with about 80 amps for your MD (27 amps per phase if you have 3 phase). You may save a little bit in the cable cost. Let me reiterate the socket outlet part of the MD calc: Upstairs <60 = 25 amps. Downstairs <40 = 20 amps. Under your circumstances, this seems to be quite resonable given that each socket outlet is rated at 10 amps. Your "after diversity calculation" arrived at a total of 45 amps for <120 socket outlets. The method used to calculate your MD is one of 4 methods available (yours was "calculation"). The other methods are: 1] Assessment. 2] Measurement. 3] Limitation. Assessment is the most difficult to do...especially in a domestic situation because people tend to change their habits etc. Also, when new family members arrive (babies etc), this causes yet another change. Measurement is possible but it will only be of any use if the current used is monitored over a long period (months or better yet, 1 year). The limitation method is simple but very expensive...even more expensive than your current calculation. From the Standard; Quote Where more than one item of equipment is connected, the circuit current could be simply assessed as the sum of the individual equipment load currents. While this would provide a safe and conservative solution, it does not take account of the normal operating conditions during which all equipment is not operating simultaneously at full load or for long periods, e.g. submains to a distribution board associated with numerous socket outlet circuits. Under such conditions the circuit current is estimated using diversity factors and is often described as the 'after diversity maximum demand'. The diversity factors applicable to any given circuit in an installation will depend on a number of features of the installation including— [a] conditions under which the installation is expected to be used, e.g. residential compared with commercial; and [b] operating characteristics of the connected load, e.g. airconditioning load in tropical locations compared with heating loads in cold-climate regions; and [c] number and physical distribution of points provided on the circuit, e.g. socket-outlets provided for convenient connection of portable equipment compared to dedicated or fixed equipment loads; and [d] size and type of significant loads, e.g. large motors or industrial plant. It should be recognized that the determination of diversity factors is not accurate for every installation and different installations of the same type may have significantly different load profiles which the designer needs to consider. The methods provided herein have been used over several editions of AS/NZS 3000 and, provided that care is taken to assess the presence of unusual equipment loads, are considered appropriate for many typical applications. When the load is assessed and the current-carrying capacity of the circuit is determined by allowing for diversity of operation of equipment, then the circuit should be protected by a circuit-breaker of rating to comply with Paragraph B3.2. If you wish to gamble, that's up to you. When it comes to electrical, I trust a tried & tested standard. The 5 cents you might save today may cost you a lot more in the future. BTW, electricians in Australia would end up with the same result as I did. The "not so smart" electricians tend to gamble (which means "guessing"). They do this to "win the job". Two important purposes of using "After Diversity Maximum Demand" are to avoid FUTURE situations of voltage drop & hot cables (fire). I think you have nothing to worry about. You have a valid MD calculation that has been tried, tested & otherwise proven to be safe & unproblematic. I think you really need to concentrate on what the PEA are going to do about your MD, whether you take a short cut & make it 80 amps or use the present MD of 100 amps. You need to make sure that they will use the correct cable for your installation. #64Posted 2009-11-04 09:38:39
There are only three meter sizes available in our area: 5/15, 15/45, and 30/100. I have advised the PEA of your MD calculation and they have said that I would be able to have a 30/100 meter. The issue is that 3-phase is not yet available at our location. That leaves us with three options: 1) to pay for extending their 3-phase cables to our location, 2) to pay for a transformer at our location, or 3) "tough it out" with single phase until the PEA (inevitably) brings 3-phase past our location, to service all the new constructions downstream from us. But we cannot make this decision yet, because we don't yet know the costs of options 1) and 2)
The decision that we should be able to make at this time, however, is the specification for our main supply cable. I asked the PEA and they say, "16 mm^2 (copper) should be fine, but go with 25 if that makes you feel more comfortable". Sorry, but the precision of that answer doesn't make me feel more comfortable. Furthermore, the PEA's own endorsed table indicates that 35 mm^2 (copper) is the minimum size for a 100 amp service! But worse yet, that table includes no parameter for the length of the cable! Furthermore still, I have tried at least six online cable-sizing calculators and get inconsistent answers from all of them. I am sure that much of this confusion is simply due to my own limited understanding. But for one thing their input forms don't appear to clearly distinguish between total amps and phase amps. So my bottom line: Can someone out there please help me define the specifications for our main supply cable, based upon the following assumptions: A 3-phase (30/100) meter Elk's Maximum Demand = 101 amps, extended to 50 amps/phase for conservatism 100 meter run, 80 of this underground Copper cores **(If I've missed anything, please tell me) If you use a calculator, that's fine with me, but please identify it so that I can get "grounded" with these things, and figure out why I can't get them to agree. If it is useful, here is my latest one, from an electrical engineering friend in the U.S.: **{http://www.csgnetwor...izecalc.html}** BTW, as a quick digression, for the first time today I have just fingered a sample of NYY 4-core 25 mm^2 copper cable. It is (to me anyway) a shockingly large hunk of hardware -- nearly 1-1/2 inches in diameter. And I was quoted a price of 366 THB per meter.
Also, don't get caught up in a battle with them (PEA) about paying money for transformers. Far too many foreigners fall for this trick. If you are in a "zoned" area for building, you need to find out what the electrical limitations are for your zone. I'll bet it's not a 15 amp meter! The PEA must supply you with electricity at their cost (if you are permitted to have a large supply). The exception is if you live a long way from power lines, in which case, you will pay for cable & transformer costs. FYI, typical transformer sizes in Thailand are from 20KVA for an individual installation to about 250KVA for local distribution. #65Posted 2009-11-04 19:34:31
Zap, I've calculated the type & size cable you need that allows for a voltage drop of not greater than 5% of the supply voltage (19 volts). It is made by Thai Yazaki http://www.thaiyazak...x_building.html
The size & type is 16mm squared copper, THW, MEA Type A - see the above link for pictures & other info. Just to ensure perfect clarity, you will need four (4) conductors for your consumer mains. All of these conductors will be the size & type of cable mentioned above. I also recommend that you use a minimum size conduit of 40mm & that it be buried no less than 500mm deep. This size cable will easily allow 46 amps as per the Aust Standard (AS3008.1.1:1998). The method I used is conservative so assume the cable is ok for 50 amps. In case I didn't mention it, your Main Earth cable should be no less than 6mm squared copper. This is the cable that runs from the Earth Electrode (rod) to the Earth Bar in your consumer unit. #66Posted 2009-11-05 07:21:31
Thank you, Elk,
I'm relieved to see that you are comfortable with 16mm^2 instead of that monstrous 25mm^2, 4-core that I mentioned.
Zap, I've calculated the type & size cable you need that allows for a voltage drop of not greater than 5% of the supply voltage (19 volts). It is made by Thai Yazaki http://www.thaiyazak...x_building.html The size & type is 16mm squared copper, THW, MEA Type A - see the above link for pictures & other info. Check Just to ensure perfect clarity, you will need four (4) conductors for your consumer mains. Check All of these conductors will be the size & type of cable mentioned above. I also recommend that you use a minimum size conduit of 40mm & that it be buried no less than 500mm deep. For some reason I had pictured in my mind that I would need a single 4-core cable, whereas you are specifying four single-core cables. Can you please clarify the issues at play? This size cable will easily allow 46 amps as per the Aust Standard (AS3008.1.1:1998). The method I used is conservative so assume the cable is ok for 50 amps. In case I didn't mention it, your Main Earth cable should be no less than 6mm squared copper. This is the cable that runs from the Earth Electrode (rod) to the Earth Bar in your consumer unit. I should be O.K. here -- this cable is 25 mm^2! #67Posted 2009-11-06 22:32:02
For some reason I had pictured in my mind that I would need a single 4-core cable, whereas you are specifying four single-core cables. Can you please clarify the issues at play? Finally, I have searched, but cannot find, a table that defines the codes/ratings THW, VAF, NYY, etc. Can you please tell me where to look? Four (4) individual cores may be cheaper than a multicore cable. Also, if you have an electrical problem with a multicore cable, the whole cable will need to be replaced whereas with individual cores, each affected core need only be replaced. Ratings for the cable I mentioned are in the following link; http://www.thaiyazak...hw_meatypea.pdf #68Posted 2009-11-09 12:18:25
Thank you, Elk.
I keep thinking that I should be thinking about surge suppression. I'm aware that there are devices for this purpose but I know little about them. Do the HRC fuses that you recommend help with this concern? Or is their purpose completely different? Also, since I am tied into the telco for DSL internet service, it would seem like I should have surge suppression on my phone line also. If I am wrong on either or both counts, please tell me; or, if you agree, can you (or anybody) recommend any make/models of devices that you have had good experience with? Thank you very much, ~~z
I have searched, but cannot find, a table that defines the codes/ratings THW, VAF, NYY, etc. Can you please tell me where to look? #69Posted 2009-11-10 08:39:54
Hi David96,
Finally, in reply to your post below of some days ago. The PEA came out yesterday and affirmed that the local transformer is 50KVA. He said several things that just didn't make sense to me; (I have this trouble anyway He indicated that I could have the (expensive) 30/100 3-phase meter if I wanted it, but said that he felt that a 15/45 meter would be adequate. Well, I thought that 45 max/phase would be pretty close to Elk's 50/phase, so let's talk about this (as an example.) He affirmed that this meter would accept up to 45/phase. So, 3 x 45 = 135 doesn't it? This is 35% over Elk's MaxDemand calculation of 101 amps. So why not consider it? At this point he visibly pulled back and said, "Oh, no, the total maximum amps from this meter could not exceed 45." And this is when he cited his small 50KVA transformer. Well, maybe I missed something in the translation, but I have been told more than once, by several different people, that I should be able to pull up to the full 45 amps/phase, (total 135), (at least for short periods), from this meter. Now I am completely confused. A complete contradiction. Can you, (or anyone), give me an explanation that hangs together with the above statements -- or am I completely misunderstanding something?
Strange that the PEA does not know the size in KVA of the distribution transformer it is usually stamped on the side of the transformer and can be read from the ground. 50KVA and 100KVA are common sizes for distribution transformers. It is obvious that from your MD you may have to go to a 3 phase supply. Otherwise it is 22kw all on one phase or balance 22kw over 3 phases. ie approx 7kw per phase. And if the PEA transformer is found to be too small it would have to be upgraded. #70Posted 2009-11-10 21:25:53
Wow you guys are comprehensive!
May I sugest UN Electric in Bangkok as a cheap source of wire. Ask for K. USA ..she speaks English. Make sure you get a high quality ground rod / copper encased steel 10' x 5/8" and if you can get someone with a ground resistance meter check the soil..Should be 1 ohm. I f higher ..more rods or special gound soil..avail in BKk Surge protect everything tv, phone lines , main panel. These simple steps will protect the expensive componets in your home. Jack #71Posted 2009-11-11 06:04:11
Hi David96, Finally, in reply to your post below of some days ago. The PEA came out yesterday and affirmed that the local transformer is 50KVA. He said several things that just didn't make sense to me; (I have this trouble anyway He indicated that I could have the (expensive) 30/100 3-phase meter if I wanted it, but said that he felt that a 15/45 meter would be adequate. Well, I thought that 45 max/phase would be pretty close to Elk's 50/phase, so let's talk about this (as an example.) He affirmed that this meter would accept up to 45/phase. So, 3 x 45 = 135 doesn't it? This is 35% over Elk's MaxDemand calculation of 101 amps. So why not consider it? At this point he visibly pulled back and said, "Oh, no, the total maximum amps from this meter could not exceed 45." And this is when he cited his small 50KVA transformer. Well, maybe I missed something in the translation, but I have been told more than once, by several different people, that I should be able to pull up to the full 45 amps/phase, (total 135), (at least for short periods), from this meter. Now I am completely confused. A complete contradiction. Can you, (or anyone), give me an explanation that hangs together with the above statements -- or am I completely misunderstanding something?
Strange that the PEA does not know the size in KVA of the distribution transformer it is usually stamped on the side of the transformer and can be read from the ground. 50KVA and 100KVA are common sizes for distribution transformers. It is obvious that from your MD you may have to go to a 3 phase supply. Otherwise it is 22kw all on one phase or balance 22kw over 3 phases. ie approx 7kw per phase. And if the PEA transformer is found to be too small it would have to be upgraded. A distribution transformer rated at 50KVA 220/380 volts will supply 76 amps per phase. This has to supply all existing consumers supplied off this transformer. When you add your max demand as calculated ( 34 amps per phase) it will be obvious that the transformer will be overloaded. The PEA will have to upgrade (replace) the existing transformer with a larger one eg, 100KVA. This will supply 150 amps per phase. A 10/45 meter will carry 45 amps continuous, they are calibrated at 10 amps.So you could have 3 x 10/45 meters, one for each phase or 1 x 3 phase 10/45 meter. This would depend on the policy of the PEA. Now whether the PEA want you to fund some of the capital cost of the upgrade is another matter. It would appear that you should not have to bare the cost except for the initial connection to supply. #72Posted 2009-11-11 07:37:06
Just a note on energy metering.
The ratings of a kWh meter. eg 10/45. The first figure is the current in amps that it is calibrated at. The second figure is the max continuous load current in amps that it will carry without affecting the accuracy of the meter. The revs per kWh is taken at a load of 10 amps or the first figure. The first figure may be 5 ( 5/15 ) or 30 ( 30/100) for example. Where the load is large eg 200A per phase or more current transformer metering is used. The meters are rated 5/200, 5/400, etc. This means they have a max 5 amps though the meter for measurement purposes, revs per kWh is taken at 5 amps. Meters may be single phase or three phase. The size of the meter in amps does not affect the total amps that one can use, this is dependant on the size of the distribution transformer, and your demand on the transformer in amps at any given time. Energy meters remain the property of the supply authority, one does not "buy" a meter in this case the "connection to supply fee" covers the cost of supplying a meter. #73Posted 2009-11-11 17:08:36
Thank you, Elk. I keep thinking that I should be thinking about surge suppression. I'm aware that there are devices for this purpose but I know little about them. Do the HRC fuses that you recommend help with this concern? Or is their purpose completely different? Also, since I am tied into the telco for DSL internet service, it would seem like I should have surge suppression on my phone line also. If I am wrong on either or both counts, please tell me; or, if you agree, can you (or anybody) recommend any make/models of devices that you have had good experience with? Thank you very much, ~~z
I have searched, but cannot find, a table that defines the codes/ratings THW, VAF, NYY, etc. Can you please tell me where to look? Hi Zap. HRC fuses will not protect an installation from any electrical surges. This page may shed some light on Surge Protection for you. http://www.novaris.c...wer/index.shtml To protect your power, I'd recommend something like this; http://www.novaris.c...ple_phase.shtml To protect your phones etc, I'd go for something like this; http://www.novaris.c...rotection.shtml The products shown are high quality & are probably not available in Thailand. The technical info on the pages can be used to source such equipment in Thailand. In one of the Square D catalogs (Square D catalog 08 - page 11 to page 20), surge protection equipment is shown. Not enough information is shown to decide if this is what you need. The device is on page 6. Its part number is QO-SPD225. David has done a pretty good job of covering your KWH meter questions #74Posted 2009-11-12 06:28:02
Hi Zapatero,
One finds it unusual that the PEA does not look at and calculate the maximum demand in amps, and then see if the distribution transformer can handle the extra proposed load. Supplying a 3 phase 45 amp energy meter (15/45) is correct if the MD is less than this figure and the distribution transformer can handle the extra load but supplying a 15/45 amp meter and then implying that you can have a load of 45 amps per phase when in fact the transformer cannot supply this extra load is misleading and the PEA is avoiding their responsibilities. Your electrician should be capable of approaching the PEA on your behalf and be able to advise them of the proposed loading (MD) and they should be able to advise what the actual conditions of supply are for your installation. In your case the MD has been calculated using AS3000/2007. How maximum demand calculations are made in Thailand may be completely different or more than likely in the case of residential installations ignored altogether in the case of the PEA or they just say that the MD is the max continuous rating of the meter (45A) and ignore the fact of the extra load on the distribution transformer and if it is capable of supplying it. The standard meter for most Thai residential installations is single phase 5/15A. #75Posted 2009-11-14 08:27:51
Hi David96,
Thank you for this, and for your previous post on energy metering -- that helped me clear up some misconceptions.
Hi Zapatero, One finds it unusual that the PEA does not look at and calculate the maximum demand in amps, and then see if the distribution transformer can handle the extra proposed load.
Supplying a 3 phase 45 amp energy meter (15/45) is correct if the MD is less than this figure and the distribution transformer can handle the extra load but supplying a 15/45 amp meter and then implying that you can have a load of 45 amps per phase when in fact the transformer cannot supply this extra load is misleading and the PEA is avoiding their responsibilities.
Your electrician should be capable of approaching the PEA on your behalf and be able to advise them of the proposed loading (MD) and they should be able to advise what the actual conditions of supply are for your installation.
In your case the MD has been calculated using AS3000/2007. How maximum demand calculations are made in Thailand may be completely different or more than likely in the case of residential installations ignored altogether in the case of the PEA or they just say that the MD is the max continuous rating of the meter (45A) and ignore the fact of the extra load on the distribution transformer and if it is capable of supplying it. In summary, I guess it boils down to what Elk says: Advise the PEA of everything, including the proper MD calculation that was done. (And I have done this.) And make sure that my own wiring and main feed cables are consistent with that MD calculation, and then let PEA do what they wish. And if their meter burns out then it won't be my fault. (Side note: I should say, in the PEA's defense, that they have been very congenial and positive -- they just haven't been very rigorous in their conclusions, or precise in their recommendations.) |