Posted 2009-10-28 08:11:28

This is quite a lengthy post… so please sit back and relax.

        I've taken some time to read a number of threads in the Thai Visa Forums  discussing the availability, operation and certain technical aspects of  electrical generators in Thailand.

        The aim of this post is to collate some of the questions previously  posed into a single thread and offer additional information for anybody  considering the purchase of a generator. I hope that this thread will also  serve as a focal point for future generator related questions or comments for  the benefit of all interested readers.

        Regardless of size, a comprehensive range of generators are available in  Thailand; from cheap and nasty, to the best that money can buy… in the last 12  months I have had meetings with a number of major metropolitan generator  distributors and OEM assemblers in an attempt to better understand the  generator market in Thailand, with a view to rolling out a comprehensive  service in 2011.

        Most of the products produced by big name engine and alternator  manufacturers are imported and available in Thailand; Caterpillar, Cummins,  Lister, Deutz, Perkins, Volvo, Scania and John Deere engines… Leroy Somer, Mecc  Alte Spa and Stamford  alternators to name a few… they're all available, if you're willing to pay the  price; and after import duty, distributor mark up and VAT, they're not cheap.

        We all know that the average expatriate in Thailand is a thrifty species; we  invariably want European or American quality at a Thai price, but during the  occasional sane moment, most of us still realize that we do actually get what  we pay for in this life… My NZ neighbour (hi John…) is quite vocal on the  locally manufactured items he's purchased, that have gone t*ts up in the last  couple of years. He's so anxious to purchase quality items that he resembles a  pack horse each time he returns from NZ or AU.

        Having trawled extensively through the domestic generator market in an  attempt to sort the wheat from the chaff, I will follow this post with examples  of a line of generators currently available in Thailand. They represent neither  the best, nor the worst generators available in Thailand, I have chosen them because in my opinion, they offer a good combination of quality and reliability at a reasonable and  realistic price.

        For the purpose of this post and in the interest of clarity; an  alternator is the AC power generating portion, of what is commonly referred to  as a 'generator'. Engine, refers to the mechanical power source, directly or  indirectly driving the alternator, and generator refers to the combination of  the two individual component parts.

        What follows is an attempt to explain common generator terminology and  identify some important aspects of generator operation and control.

    Diesel  or petrol (gasoline) powered generator engines, what's the difference and which  one is the best option…?

  • A diesel       engine burns less fuel than a petrol engine performing the same work, due       to the engine's high efficiency.
  • A diesel       engine has no high-tension       electrical ignition system to attend to, resulting in high reliability and       easy adaptation to damp environments.
  • A petrol       engine uses a spark plug to ignite a fuel/air mixture in the combustion       chamber, driving a piston which powers the crankshaft. A diesel engine       uses the heat of compression alone to initiate ignition and achieve the       same effect.
  • The life of a diesel engine is generally about       twice as long as that of petrol engines, due to the increased       strength of parts used, also because diesel fuel has better lubrication       properties than petrol.
  • Diesel fuel is considered safer than petrol in       many applications. Although diesel fuel will burn in open air using a       wick, it will not explode and does not release a large amount of flammable       vapour.
  • The carbon monoxide content of diesel engine       exhaust is minimal as opposed to the high carbon monoxide content of       petrol exhaust.
  • Petrol driven generators are generally used to       drive alternators up to 10Kva in size.
  • Increased fuel economy, lower engine speeds       and overall reliability make diesel the preferred choice for generator       engines driving alternators over 10Kva in size.
What's the difference between direct  drive and belt driven generators?

        
  • A direct drive generator has the alternator       bolted directly to the flywheel of the engine, in this configuration the       alternator is single bearing.
  • Direct drive is the most efficient method of       driving an alternator.
  • A twin       bearing alternator with pulley is required if the alternator is to be belt       driven. Depending on the available RPM of the engine and whether the       alternator is 2 or 4 pole, a gearbox may also be required to achieve the       correct RPM to drive the alternator.
  • Belt driven       alternators may be up to 50% less efficient than direct drive.

Alternators;  2 pole or 4 pole, what does this mean and what's the difference...?
  • 'Pole'       refers to the permanent or (more commonly) electro magnets mounted on the       rotor within the alternator. A 2 pole alternator has 2 magnets, a 4 pole       alternator; surprise, surprise… has 4.
        Engine  RPM, why do some generators operate at 1500rpm, others at 3000rpm (not to  mention 1800, 3600rpm and 4500rpm etc…)?

        
  • Single       phase utility supply in Thailand       is 220v @ 50Hz, the phase to phase voltage of three phase utility supply       is 380v @ 50Hz.
  • The       frequency of a generator supply is dictated by the speed of alternator       rotation.
  • For a 2       pole alternator 600rpm = 10Hz, for a 4 pole alternator 300rpm = 10Hz.
  • Thus a       single phase 2 pole alternator must rotate at 3000rpm to generate 220v @       50Hz (If this generator were in the US, it would rotate at 3600rpm       for 60Hz). A three phase 4 pole alternator with twice the number of magnet       poles only has to rotate at half the speed of the 2 pole alternator to       generate the same voltage and frequency, 1500rpm would generate 220v       (phase to neutral) and 380v (phase to phase) @ 50Hz (and again, in the US,       it would rotate at 1800rpm for 60Hz).
        I've  seen some generators rated in Kva and others in Kw… What's the difference?

        
  • Kva       (Kilovolt Ampere) relates to 'apparent power' and Kw (Kilowatt) to 'actual       power', the difference is related to Power Factor, and is a consideration when part of the load is comprised of AC motors in appliances such as refrigerators, ac units, well pumps etc.
  • As most homes contain appliances such as this, typically, we will calculate the maximum Kw rating of a generator by       multiplying the Kva value by a power factor of 0.8 to take the motors into account; e.g. 30Kva x 0.8 = 24Kw... this is the maximum available power, on which you should base your load calculation.
  • If you are       technically minded and would like to read more about the difference between       Kva and Kw the following is a good article; http://rep.mgeups.co...technote/kw.pdf
        What  is an AVR and how does it work?

        
  • Electronic voltage regulation is finding its       way into smaller and smaller generator sets these days.
  • It is still common for the voltage of small       portable generators, to be regulated by a capacitor which will regulate       the generator voltage within 5 to 10% of that required. An electronic AVR       (automatic voltage regulator) is a far better option and will regulate the       voltage within 1 to 2% or better.
  • An AVR works by converting a small amount of       the generator AC voltage to DC current (once the generator is at full       voltage).
  • This current is inversely proportional to the       generators output voltage (the higher the voltage output of the generator,       the less DC current the voltage regulator produces).
  • AVRs are normally adjustable allowing voltage       to be accurately set when the generator is running at full speed with no       load. When a load is added to the generator, the output voltage will drop       a little. The AVR instantly compensates by increasing the amount of DC       current to the field coils, raising the voltage back to its pre-set level       and preventing voltage drop. This is especially useful for motors       requiring a surge of power on start up, such as those found in       refrigerators and air conditioning units etc.
  • With a constant, non variable load on the       generator, the voltage regulator produces just enough DC current to keep       the generator producing the correct output voltage.
        Generator maintenance… do I really  need to service this thing…? My mates genny has been running non stop for 5  years and all he does is fill her up every day or two…

        
  • The short       answer is yes…! A good quality generator represents a significant capital       investment. With regular periodical maintenance, it should give you years       of reliable service. As with any type of engine, the longer you ignore       maintenance the more serious and costly the inevitable problems will be.
  • You (or a       diesel engineer) should carry out a full service (change oil, change oil       filter, change fuel filter, clean or change air filter, drain and replace       engine coolant, check fan belt for wear and tension) annually or every 500       hours, whichever comes first.
  • Given the       average ambient temperature in Thailand, I would recommend       the use of SAE 15W-40 diesel engine oil.
  • Always use       a 50/50 mix of good quality ethylene glycol or propylene glycol coolant       with water, DO NOT use water alone. Glycol based coolants (commonly       referred to as anti-freeze, do not only offer low temperature protection       (but also improve cooling qualities in high temperature environments.       Using water alone may cause scaling, cavitation, iron corrosion and       foaming which may in turn affect engine performance, reliability and       service life.
        Brushes…Brushless…?  What does this mean and what's the difference?

        
  • Whether an alternator incorporates brushes or       not in its design, relates to the manner by which DC excitation voltage is       transferred to the rotor field windings. The rotor field windings are       mounted on a shaft (the rotor) which turns inside the stationary outer       casing containing the output windings (the stator).
  • In the majority of alternators the magnets on       the rotor are not permanent magnets, they are electro magnets which are       activated when DC voltage (excitation voltage) passes through the windings       around them.
  • An alternator with brushes transfers DC       voltage via stationary carbon brushes to slip rings on the rotor shaft       then onto the rotor field windings.
  • Some brushless alternators feature an exciter       coil which is a mini alternator normally mounted on the rear of the rotor.       DC voltage from the AVR is fed into the exciter coil, stimulating the       production of AC voltage, this passes through a rotating rectifier       arrangement, converting the AC voltage back into DC voltage and on to the       rotor field windings.
  • Whichever method is used, the DC voltage       passes through the rotor field windings and activates the electro magnets.       As the electro magnets rotate, they induce AC voltage in the stator       windings and power is produced, more information on how an alternator       produces AC power can be found here http://www.generator...ower/4534128464
        My other mate… :)  runs his  house on a portable genny… I've seen them for sale in the local hardware store;  Sod it, I'm going to buy one of those things…

        
  • A portable       generator may indeed be just what you need… but if you want a reliable       standby power source for your home or business that will stand the test of       time and do the job properly, it is imperative that you size the generator       correctly before you jump in and buy one.
  • Ideally,       your generator should be able to handle the full load of your home or       business (or everything you wish to power) at approx 70 to 80% of the       alternators maximum load rating.
  • So, if       (with every electrical appliance you wish to operate turned on), your       home/business draws a total of 45amps; a 10Kw (approx 12Kva) generator       would be an ideal size.
  • Assuming       your home/business uses a single phase supply, the figure of 10Kw is       calculated as follows; 220v x 45amps x 0.8 power factor/1000 = 7.92 or       8Kw, this is your maximum load in Kw. An 8Kw load is 80% of the maximum       load rating of a 10Kw generator, which is thus the optimum size generator       for a 45amp load.
  • More       information on generator sizing can be found here http://www.generator...zing/4534128467
  • This may       seem a tad convoluted, but with good reason. Operating your generator at       between 70 and 80% of it's maximum load rating will burn less fuel, create       less noise, reduce engine wear and increase the engine life, allow for       growth in your electrical needs (the purchase of an additional TV, fridge       etc) and most importantly, reduce the likelihood of damage to, or       catastrophic failure of the alternator.
  • As the       alternator reaches its maximum rated output, the temperature within the       alternator windings will rise dramatically. The thermal insulation of       every alternator is rated according to its ability to withstand the heat       generated as an alternator begins to overload (this is what happens every       time you load any generator to the gills, or continuously operate a       generator at close to its maximum rated output).
  • If an       overload is sustained, the insulation will eventually fail and the       alternator will short and burn out (unless the over current trips the       generator breaker (if fitted) and saves the alternator), this is normally       accompanied by a mass of sparks and black, acrid smoke, pouring out of the       alternator air vents.
  • Depending       on the degree of damage; rewinding the alternator (time consuming and       relatively expensive), or simply changing it out for a new alternator       (again, an expensive and time consuming exercise) are the only options       available.
  • Taking the       time to calculate the load requirement of your home/business and correctly       selecting a generator based on the aforementioned calculation is highly       recommended. It is an economic blunder to simply buy a portable generator       just because it's cheap… a thoughtful selection process will not only save       you time and money, but ensure that you get the best out of your generator       investment over the long term.
        How  do I connect the generator to my distribution board…?

        
  • If you are       purchasing a generator as a standby power source for your home, the       connection between the generator and your consumer unit/distribution board       MUST be made through a manual       or automatic transfer switch (I would recommend these connections be made       by a qualified electrician). Under no circumstances should you ever       attempt to connect the generator directly to your consumer       unit/distribution board.
  • Connecting       the mains and generator supply simultaneously requires a complex       synchronization process, but this is an expensive option and not required       for general automatic mains failure use.
  • More       information on how a transfer switch works can be found here http://www.generator...rols/4534128482
        
All generators fall into one of four distinct categories (ratings) according to  use (as defined in ISO 8528-1:2005). Each category is listed below together with examples  of generator types for home use and other applications (petrol and diesel driven versions only).

        Emergency Standby Power  (ESP)  – Variable Load - 200 hours per  year.

        
  • Light duty,       lightweight and portable (tubular frame design or the like).
  • Single cylinder,       air cooled engine.
  • Predominantly       petrol driven, although diesel versions are becoming more common (and are slightly       more expensive).
  • Single       phase, 2 pole alternator driven at 3000/4600rpm depending on size, for       50Hz.
  • May feature       a low oil pressure shutdown switch.
  • Recoil hand       starter/crank starter or 12v DC electric start.
  • Generally       feature alternators up to 10Kva/8Kw in size and are designed to produce up       to the alternators maximum rated output for 200 hours a year with       no overload capacity.
  • Capacitor       voltage regulation (5 to 10%) or electronic AVR on more expensive models       (1 to 2% or better).
  • Power is       distributed via on board plug sockets. This type of generator is not       designed (with one or two notable exceptions) to operate in combination       with an automatic transfer switch.
  • Common       applications; static construction sites/work tool power source, RV standby       power, emergency lighting supply, etc.
        Limited Time Running Power  (LRP) (commonly referred to as Standby Power) – Constant Load - 500 hours per year.

        
  • Heavier       duty, mounted on a chassis/skid, permanent installation.
  • Multiple       cylinder, diesel powered, water cooled engine (intercooler and/or turbo       may feature on larger engines).
  • Single or       three phase, 2 or 4 pole alternator driven at 3000 or 1500rpm respectively       for 50Hz (certain types of alternator may be optionally configured as       either single or three phase).
  • May feature       low oil pressure, high temperature and low coolant level shutdown       switches.
  • 12 or 24v       DC electric start (depending on size).
  • Generally       feature alternators in the 10 to 30Kva/8 to 24kw range depending on the capability of the engine, alternator insulation grade etc, and are designed       to produce up to their maximum rated output for 500 hours a year with no       sustained overload capacity.
  • Alternator       overload protection is provided and power is distributed, via a generator       mounted circuit breaker.
  • Voltage       regulation provided by electronic AVR.
  • Will       normally feature an electronic control panel with additional       protections/alarms (low/high frequency, low/high voltage, under/over       speed, low oil pressure, high temperature, low coolant level, low fuel       level etc).
  • May feature       a remote start option and be compatible with an Automatic Transfer Switch.
  • Common       applications; a generator permanently installed as a standby/secondary       source of power for a mid sized home or business and rated to operate for       the average duration of a utility power outage.
        Prime Power (PRP) –  Variable Load - Unlimited Hours

        
  • Engine and       alternator features are as per the LRP rating; but as reliability and       power generating demands increase, the tolerance of manufactured materials       and assembly of component parts must increase.
  • Unlimited run time; a prime power rated generator may supply up to it's maximum rated output 24hrs a day on a variable load. Typically, a 10% overload is permitted for up to one hour in any 12hr period.
  • Common       applications; a generator permanently installed as a prime source of power       in place of a utility power supply (e.g. a remote location with no utility       supply) and rated to produce up to the alternators maximum rated output for an unlimited period       of time.
        Continuous Power (COP) –  Constant Load - Unlimited Hours

        
  • Engine and       alternator features as per the PRP rating; but as reliability and power       generating demands increase, the tolerance of manufactured materials and       assembly of component parts must increase.
  • Unlimited run time; a continuous power rated generator may supply its continuous rated output 24hrs a day to a constant (base) load and no overload is permitted.
  • Common       applications; a generator permanently installed and synchronized to feed       power into and support the national grid supply and rated to produce       the alternators maximum rated output for an unlimited period of time.
After deciding on a line of generators that I felt offered the best  quality/price combination, I contacted the manufacturer and they agreed to  allow me to import their machines into Thailand beginning 2011. Although  generators up to 375Kva in size are available from the manufacturer, for most people,  the first two categories; Emergency Standby Power and Limited Time Running  Power, will be of interest and they will therefore be my focus.

        That doesn't help much if you're in the market for a decent generator  today of course... In an attempt to provide an interim solution to the  availability and supply of good quality generators for the expatriate  community, I decided to reach out to one of their existing distributors.

        There are two existing distributors in Thailand, I have met with both and  established a good relationship with one in particular. They have agreed (in  lieu of a commission payment to me), to offer these generators to the  expatriate community, at a much lower price than their competitor. Lower in  fact, than the price they are available to Thai nationals walking in off the  street…imagine that..! One stipulation is that to receive the prices posted  below, all referrals to the distributor in question should come through my  website.

        I will not receive any commission or payment in kind for these  referrals… It may seem a little crazy for me to promote these generators for no  financial gain, but until such time as I begin to import and sell this line of  generators myself in 2011; This arrangement will allow me to establish a  relationship and network with Thai distributors, raise the profile of these  generators in Thailand, raise the profile of my website and hopefully present  the expatriate community here, with an opportunity to purchase a quality  product at a fair price, a win, win situation for all concerned I hope.

        Congratulations if you've managed to read to the end of this post… my  eyeballs are ready to leap out of my head and roll for cover at the thought of  me typing any more to be honest…

        More information on my website @ www.generatorsolutions.org and  you can contact me directly @ john@generatorsolutions.org  

        If you decide to respond to this post, please delete my original post  from your reply, or we could spend all day scrolling…

        Regards,

        Genset

Edited by genset, 2009-11-15 07:14:01.


#2 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-28 08:16:12




IG2000  – Emergency Standby Generator

        
  • Very       portable, lightweight set weighing only 22kg, sleek clean design.
  • Manufactured       to CE standards (EU Machinery Directive 98/37EC and EU Low Voltage Directive 2006/95/EEC)
  • EPA certified  , the high efficiency combustion system results in ultra low emissions.
  • Available       in 1Kva (800watt), 2Kva (1.6Kw) and 2.6Kva (2.08Kw) sizes and suitable for       a wide range of applications.
  • Low noise design, 54~59db/7m on a full load.
  • Inverter technology delivers quality output.
  • Unique and patented air cycle system.
  • Single       cylinder, 4 stroke, OHC petrol engine.
  • IG2000       (pictured) Operates at 4500rpm, single phase, 230v @ 50Hz and delivering       approx 7 amps of usable power (IG1000 4600rpm 3.9 amps – IG2600 3600rpm 10       amps) or 12.3amps DC.
  • Recoil       starter.
  • 3.5 hours       runtime when loaded and fully fuelled.
  • Set must be       grounded if used to power a grounded load.
  • 12 months       warranty.
    Prices including VAT from distributor;

        IG1000 – 15,000 Thb

    IG2000 – 19,000 Thb

    IG2600  - 23,000 Thb

        These  generators can also be seen on my website at http://www.generator...ator/4534282010

    

Attached Files


Edited by genset, 2009-12-11 13:43:47.


#3 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-28 08:19:20




    KDE6700TA - Emergency  Standby Generator


    
  • Mobile set, on       wheels, sturdy, well built, weighs 193kg.
  • Manufactured       to CE standards (EU Machinery Directive 98/37EC and EU Low Voltage Directive 2006/95/EEC).
  • 4.5Kva (3.6Kw),       suitable for a wide range of applications.
  • Generator       is enclosed in a soundproof canopy, unit operates at 72db/7m on a full       load.
  • Electronic       AVR voltage regulation.
  • Brushless,       self exciting, 2 pole alternator.
  • Air cooled,       single cylinder, vertical four stroke direct injection diesel engine.
  • KDE6700TA       operates at 3000rpm producing single phase, 230v @ 50Hz and delivering       approx 19.6amps of usable power.
  • Electric       start, the set also features a digital control panel with a remote start       facility.
  • Set has ATS       connections and is compatible for use with an automatic transfer switch.       This enables completely automated operation in the event of a power       failure or deep brown out to your home.
  • 9.5 hours       runtime when loaded and fully fuelled.
  • Set must be       grounded if used to power a grounded load.
  • 12 months       warranty.
        Price  including VAT from distributor;

        KDE6700TA  – 54,000 Thb

        These generators can also be seen on my  website at  http://www.generator...ator/4534282010

Attached Files


Edited by genset, 2009-11-01 00:00:19.


#4 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-28 08:21:44




    KDE12STA  – (LRP) Limited Time Running Power (commonly referred to as Standby Power) Generator.


    
  • Static set,       in soundproof canopy, on skids, weighs 345kg.
  • Manufactured       to CE standards (EU Machinery Directive 98/37EC and EU Low Voltage Directive 2006/95/EEC).
  • 8.5Kva       (6.8Kw), suitable for a wide range of applications.
  • Enclosed in       a soundproof canopy, unit operates at 72db/7m on a full load.
  • Electronic       AVR voltage regulation.
  • Brushless,       self exciting, 2 pole alternator.
  • In-line V       twin, four-stroke, water cooled, direct injection diesel engine.
  • KDE12STA       operates at 3000rpm, producing single phase, 230v @ 50Hz, and delivering       approx 36.9 amps of useable power.
  • Electric       start, the set also features a digital control panel with a remote start       facility and additional features such as a periodical exerciser function.
  • Set has ATS       connections and is compatible for use with an automatic transfer switch.       This enables completely automated operation in the event of a power       failure or deep brown out.
  • 7.5 hours       runtime when loaded and fully fuelled.
  • Set must be       grounded.
  • 12 months       warranty.
        Price  including VAT from distributor;

        KDE12STA  – 110,000 Thb

        These generators can also be seen on my  website at http://www.generator...ator/4534282010
    

Attached Files


Edited by genset, 2009-11-08 02:22:13.


#5 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-28 08:25:21




KDE16SS – 13Kva Rated as a PRP Generator (Prime Power)

        
  • Significant       step up in performance and reliability. Static set, in Super Silent canopy,       on skids, weighs 790Kg.
  • Manufactured       to CE standards (EU Machinery Directive 98/37EC and EU Low Voltage Directive 2006/95/ EEC).
  • 13Kva       (10.4Kw as a PRP set),15.5Kva (12.4Kw as an LRP set); suitable for a wide range of       applications. This set will easily power a large home, with AC's, and       numerous electronic appliances.
  • This is a       Super Silent Generator set, enclosed in a well constructed soundproof       canopy; unit operates at 51db/7m on a full load, very quiet.
  • Electronic       AVR voltage regulation.
  • Brushless,       self exciting, 4 pole alternator.
  • In-line 4       cylinder, four-stroke, water cooled, direct injection diesel engine.
  • KDE16SS       operates at 1500rpm, producing single phase, 230v @ 50Hz, and delivering       approx 56.5 amps of useable power as a PRP set and approx 67.4 amps of useable power as an LRP set.
  • Electric       start, the unit also features a digital control panel with a remote start       facility and additional features such as a periodical exerciser function.
  • Unit       features ATS connections and is compatible for use with an automatic       transfer switch. This enables completely automated operation in the event       of a power failure or deep brown out.
  • 11 hours       runtime when loaded and fully fuelled.
  • Access       points for fuelling, adding coolant etc are conveniently located on the       exterior of the generator canopy. Taps to drain and refill engine oil are       conveniently located along the skid for ease of maintenance.
  • Unit must       be grounded.
  • 12 months       warranty.
        Price  including VAT from distributor;

            KDE16SS  – 201,000 Thb

    

These generators can also be seen on my  website at http://www.generator...ator/4534282010

Attached Files


Edited by genset, 2009-11-08 02:52:52.


#6 Artisi

Artisi

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,711 posts

Posted 2009-10-28 12:02:05

Excellent post, well put together in a logical, precise and informative manner - trust those in need of a genset take the time to read it carefully.

I think it would be good if the "powers that be" could make this a Forum topic so it is not lost in with the hundreds of other postings.

#7 tjo o tjim

tjo o tjim

    Senior Member

  • Members
  • PipPipPipPip
  • 460 posts

Posted 2009-10-28 12:17:17

Nice write-up; you managed to cover a number of difficult topics in plain language.

On these little gensets, what level of leading power factor can they support?  Too many of the electronic AVR systems seem to choke on minor leading power factor (0.97 capacitive PF).

#8 joncl

joncl

    Senior Member

  • Advanced Members
  • PipPipPipPip
  • 524 posts

Posted 2009-10-28 13:15:33

One of the issues facing many people (me included) and maybe Genset might like to explain this to us in more details is;

1. Not all generator sets will  power / recharge nor work with a UPS line (AC-AC), where a DC based inverter system, will work due to their configuration (DC-AC).
2. Will your KDE6700TA - Emergency  Standby Generator recharge and can it be used with an UPS inline (AC-DC-AC) or does it have to be removed like many other generator sets require you to do?

We use UPS's here on all our system as our first line of defense for brownouts / blackouts. One thing that has annoyed me is the need to isolate the UPS from the generator set when the UPS's fail after 2 hours. Having said that in the last 12 months the generator has only been used for 2 hours as the UPS catch most of the brownouts.








#9 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-29 03:19:24

View Posttjo o tjim, on 2009-10-28 12:17:17, said:

Nice write-up; you managed to cover a number of difficult topics in plain language.

On these little gensets, what level of leading power factor can they support?  Too many of the electronic AVR systems seem to choke on minor leading power factor (0.97 capacitive PF).

Thank you for your comments.

The answer, in a nutshell, is very little. Regardless of who manufactures a generator AVR, they are all designed around the same principle.

There are others in the forum (Crossy and Elkangorito to name but two), who are better qualified to talk about the reasons why leading power factor can be an issue for electronic AVRs, but I would like to refer you to a white paper, written by  Gary Olson, Director, Power Systems Development at Cummins Power Generation.

The first two pages of this document explain very clearly 'the impact of leading power factor on synchronous alternators'.

Genset

Attached Files



#10 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-29 04:00:26

View Postjoncl, on 2009-10-28 13:15:33, said:

One of the issues facing many people (me included) and maybe Genset might like to explain this to us in more details is;

1. Not all generator sets will  power / recharge nor work with a UPS line (AC-AC), where a DC based inverter system, will work due to their configuration (DC-AC).
2. Will your KDE6700TA - Emergency  Standby Generator recharge and can it be used with an UPS inline (AC-DC-AC) or does it have to be removed like many other generator sets require you to do?

We use UPS's here on all our system as our first line of defense for brownouts / blackouts. One thing that has annoyed me is the need to isolate the UPS from the generator set when the UPS's fail after 2 hours. Having said that in the last 12 months the generator has only been used for 2 hours as the UPS catch most of the brownouts.


This is again related to the issue of leading power factor raised by Artisi and harmonics/wave form distortion. If you have used other generators to power your UPS backup systems (how many units?) with no succes, the likelihood of the KDE6700TA fairing any better is minimal. As I mentioned in the last post, all AVRs are designed around the same principle. Some UPS sytems operate ok with generators I have installed, and others experience problems.

Page two of the document attached to this post addresses the specific issue of why, under certain conditions, UPS systems fail to operate and/or the generator shuts down. The most common result of a heavy capacitive load is an increase in generator voltage, if fitted, the electronic generator control panel constantly monitors the generator voltage and will carry out an overvoltage shutdown and stop the machine.

Genset



Attached Files


Edited by genset, 2009-10-31 15:22:20.


#11 Naam

Naam

    Star Member

  • Advanced Members
  • PipPipPipPipPipPipPipPip
  • 18,093 posts

Posted 2009-10-29 08:06:33

View Postgenset, on 2009-10-28 08:25:21, said:

KDE16SS – LRP Generator (Standby power 14.5Kva) – PRP Generator (Prime power 12Kva)
    * Significant step up in performance and reliability. Static set, in Super Silent canopy, on skids, weighs 790Kg.
    * Manufactured to CE standards (EU Machinery Directive 98/37EC and EU Low Voltage Directive 2006/95/ EEC).
    * 14.5Kva (11.6Kw) (LRP) or 12Kva (9.6Kw) (PRP), suitable for a wide range of applications. This set will easily power a large home, with AC's, and numerous electronic appliances.
thanks Genset. very informative thread although "large home" is relative. my question is specific for my home which has 19 powerhungry aircons distributed evenly over three phases (only a third of them are running normally). are there no three-phase gensets in the range 15-25Kva available? the alternative would be to selectively wire the most important aircons and rooms as well as the kitchen to a single phase which would be fed by the generator.

i also don't understand why UPSs have to be disconnected when the generator is in use. i installed three different inverter sets (each with 2 batteries totalling 320 Ah) which, in case one or more phases are gone, power our water pumps, my study with various computers, my wife's study with computer and TV as well as my TV-room. besides the electronic equipment and lights two ceiling fans are connected.

is any kind "electrical soul" able to answer my question? Crossy? ElKangorito?

thanks in advance. presently i don't see the need of installing a generator but the time might come when i think it is necesssary and i want to be prepared for this eventuality.

#12 david96

david96

    Super Member

  • Banned
  • PipPipPipPipPip
  • 1,336 posts

Posted 2009-10-29 08:50:18

View PostNaam, on 2009-10-29 09:06:33, said:

View Postgenset, on 2009-10-28 08:25:21, said:

KDE16SS – LRP Generator (Standby power 14.5Kva) – PRP Generator (Prime power 12Kva)
    * Significant step up in performance and reliability. Static set, in Super Silent canopy, on skids, weighs 790Kg.
    * Manufactured to CE standards (EU Machinery Directive 98/37EC and EU Low Voltage Directive 2006/95/ EEC).
    * 14.5Kva (11.6Kw) (LRP) or 12Kva (9.6Kw) (PRP), suitable for a wide range of applications. This set will easily power a large home, with AC's, and numerous electronic appliances.
thanks Genset. very informative thread although "large home" is relative. my question is specific for my home which has 19 powerhungry aircons distributed evenly over three phases (only a third of them are running normally). are there no three-phase gensets in the range 15-25Kva available? the alternative would be to selectively wire the most important aircons and rooms as well as the kitchen to a single phase which would be fed by the generator.

i also don't understand why UPSs have to be disconnected when the generator is in use. i installed three different inverter sets (each with 2 batteries totalling 320 Ah) which, in case one or more phases are gone, power our water pumps, my study with various computers, my wife's study with computer and TV as well as my TV-room. besides the electronic equipment and lights two ceiling fans are connected.

is any kind "electrical soul" able to answer my question? Crossy? ElKangorito?

thanks in advance. presently i don't see the need of installing a generator but the time might come when i think it is necesssary and i want to be prepared for this eventuality.

A UPS should not be disconnected when the generator supply is on line.

The purpose of a UPS to to supply power to essential equipment, eg, computers etc in the period when the normal supply fails and the emergency generator connects to the load though an ATS. The period is nomally 5 secs of mains failure then the genset starts and goes on line. Total time about 20secs.

Normally most UPS systems will supply about 6 mins of power. This figure is when they are new, batteries deteriorate with age and after 2 years should be checked  and replaced. Larger units are available for specific purposes and have larger battery back up and will supply power for longer.

Switchboards may be connected for essential and non essential power. Essential power is supplied by the mains or generator, non essential power is supplied only by the mains.

#13 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-29 10:30:17

View PostNaam, on 2009-10-29 09:06:33, said:

View Postgenset, on 2009-10-28 08:25:21, said:

KDE16SS – LRP Generator (Standby power 14.5Kva) – PRP Generator (Prime power 12Kva)
    * Significant step up in performance and reliability. Static set, in Super Silent canopy, on skids, weighs 790Kg.
    * Manufactured to CE standards (EU Machinery Directive 98/37EC and EU Low Voltage Directive 2006/95/ EEC).
    * 14.5Kva (11.6Kw) (LRP) or 12Kva (9.6Kw) (PRP), suitable for a wide range of applications. This set will easily power a large home, with AC's, and numerous electronic appliances.
thanks Genset. very informative thread although "large home" is relative.

Yes, it is relative, my example of each category was offered as a rough guide only. If you want to be more specific regarding the selection of a suitably sized generator for your own home, I would refer you to the following paragraph from my original post. You will need to first determine your load requirement and then size your generator based on that figure:

My other mate… :)  runs his house on a portable genny… I've seen them for sale in the  local hardware store; Sod it, I'm going to buy one of those things…
  • A  portable generator may indeed be just what you need… but if you want a  reliable standby power source for your home or business that will stand  the test of time and do the job properly, it is imperative that you  size the generator correctly before you jump in and buy one.
  • Ideally,  your generator should be able to handle the full load of your home or  business (or everything you wish to power) at approx 70 to 80% of the  alternators maximum load rating.
  • So, if (with  every electrical appliance you wish to operate turned on), your  home/business draws a total of 45amps; a 10Kw (approx 12Kva) generator  would be an ideal size.
  • Assuming your home/business uses a  single phase supply, the figure of 10Kw is calculated as follows; 220v  x 45amps x 0.8 power factor/1000 = 7.92 or 8Kw, this is your maximum  load in Kw. An 8Kw load is 80% of the maximum load rating of a 10Kw  generator, which is thus the optimum size generator for a 45amp load.
my question is specific for my home which has 19 powerhungry aircons distributed evenly over three phases (only a third of them are running normally). are there no three-phase gensets in the range 15-25Kva available?

19 aircons... ok... doesnt the hotel you live in have a decent generator already...? Only kidding...there are indeed three phase gensets availabe in the 15-25kva range, but they are more costly as they are heavier duty, slow running (1500rpmk) gensets in the same range as the KDE16SS, the KDE20SS3 is one such model. Once you have determined your load requirement (remember to use starting wattage for your aircons in your calcuation), drop me a line and I will refer you to a specific size and model suitabe for your needs.

the alternative would be to selectively wire the most important aircons and rooms as well as the kitchen to a single phase which would be fed by the generator.

i also don't understand why UPSs have to be disconnected when the generator is in use. i installed three different inverter sets (each with 2 batteries totalling 320 Ah) which, in case one or more phases are gone, power our water pumps, my study with various computers, my wife's study with computer and TV as well as my TV-room. besides the electronic equipment and lights two ceiling fans are connected.

You shouldnt have to disconnect your UPS when the generator is in use, but under certain conditions, the UPS may contribute to the malfunction of the AVR resulting in generator shut down and/or non operation of the UPS system. Please read page two of the attached PDF file regarding UPS use with a synchronous alternator.

is any kind "electrical soul" able to answer my question? Crossy? ElKangorito?

thanks in advance. presently i don't see the need of installing a generator but the time might come when i think it is necesssary and i want to be prepared for this eventuality.

The superior man, when resting in safety, does not forget that  danger may come. When in a state of security he does not forget the  possibility of ruin. When all is orderly, he does not forget that  disorder may come. Thus his person is not endangered, and his States  and all their clans are preserved.
Confucius
Chinese philosopher & reformer  (551  - 479 BC) :D
  

Attached Files


Edited by genset, 2009-10-31 15:20:53.


#14 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-29 10:37:49

Quote

A UPS should not be disconnected when the generator supply is on line.

I believe Naam is referring to the question posed in post No8. Please read page 2 of the document I posted in answer to that question and for more information about 'leading power factor' and how, under certain conditions, it may affect UPS and generator operation.

The purpose of a UPS to to supply power to essential equipment, eg, computers etc in the period when the normal supply fails and the emergency generator connects to the load though an ATS. The period is nomally 5 secs of mains failure then the genset starts and goes on line. Total time about 20secs.

Normally most UPS systems will supply about 6 mins of power. This figure is when they are new, batteries deteriorate with age and after 2 years should be checked  and replaced. Larger units are available for specific purposes and have larger battery back up and will supply power for longer.

Switchboards may be connected for essential and non essential power. Essential power is supplied by the mains or generator, non essential power is supplied only by the mains.

Edited by genset, 2009-10-31 17:49:43.


#15 david96

david96

    Super Member

  • Banned
  • PipPipPipPipPip
  • 1,336 posts

Posted 2009-10-29 11:05:36

View Postgenset, on 2009-10-29 10:37:49, said:

Quote

A UPS should not be disconnected when the generator supply is on line.

I believe Naam is referring to the question posed in post No8. Please read page 2 of the document I posted in answer to that question for more information about 'leading power factor' and how it affects UPS and generator operation.

The purpose of a UPS to to supply power to essential equipment, eg, computers etc in the period when the normal supply fails and the emergency generator connects to the load though an ATS. The period is nomally 5 secs of mains failure then the genset starts and goes on line. Total time about 20secs.

Normally most UPS systems will supply about 6 mins of power. This figure is when they are new, batteries deteriorate with age and after 2 years should be checked  and replaced. Larger units are available for specific purposes and have larger battery back up and will supply power for longer.

Switchboards may be connected for essential and non essential power. Essential power is supplied by the mains or generator, non essential power is supplied only by the mains.

Supply Authority power factor can usually be between 0.6 and .9 lagging. A syncronous motor
can be run at a PF of 1.0. A sychronous motor can be used for PF correction.

Capacitors are normally used for PF correction eg, to improve an existing PF of 0.7 to perhaps
0.9.  O.95 is the economical limit.

In my experience you will not come across leading power factor in practice, it will be lagging as most loads are inductive not capacitive.

( Some small generators do have problems with their waveform when used to supply electronic equipment and the manufacturers advice should be obtained.)

#16 david96

david96

    Super Member

  • Banned
  • PipPipPipPipPip
  • 1,336 posts

Posted 2009-10-29 11:21:07

View Postjoncl, on 2009-10-28 13:15:33, said:

One of the issues facing many people (me included) and maybe Genset might like to explain this to us in more details is;

1. Not all generator sets will  power / recharge nor work with a UPS line (AC-AC), where a DC based inverter system, will work due to their configuration (DC-AC).
2. Will your KDE6700TA - Emergency  Standby Generator recharge and can it be used with an UPS inline (AC-DC-AC) or does it have to be removed like many other generator sets require you to do?

We use UPS's here on all our system as our first line of defense for brownouts / blackouts. One thing that has annoyed me is the need to isolate the UPS from the generator set when the UPS's fail after 2 hours. Having said that in the last 12 months the generator has only been used for 2 hours as the UPS catch most of the brownouts.







If your generator supplies the correct voltage, frequency and waveform the UPS should be connected to supply at all times as this is used to supply power to your essential equipment in the case of power supply failure. Normally this would be no more that 1 minute, that is until your standby genset goes on line.

We are looking here at a standard genset, auto start on mains failure and with a run on time of usually 15 minutes after power has been restored.

A typical genset would be 220/380 to 240/415Volts, 50Hz, 4 pole 1500 rpm.

As far as an UPS is concerned there is no difference between the mains supply and the generator supply.

#17 Gary A

Gary A

    Titanium Member

  • Advanced Members
  • PipPipPipPipPipPipPip
  • 8,974 posts

Posted 2009-10-29 11:33:44

I was determined to have a generator to power everything except the hot water shower, (5,200 watt), and the air conditioner. I have a 30 HP diesel tractor with a PTO or an 11 HP diesel Kubota to drive a generator. I have since given up on the project. I already have a small gasoline powered generator. I have found that I can make the electric come back on by using the small generator.  :)  At least it seems that way. The outages are normally quite brief. By the time I run the extension cords and get the generator running, the power comes back on.

I have now decided that I want to use a battery backup system. Just like a computer UPS but much larger. It would normally use the main to stay charged but in case of a prolonged power failure, a generator could also be used to charge the batteries. Much more expensive but automatic switching is very convenient. A capacity of about 1400 watts for a couple of hours would be enough.

Genset, are you able to put together a system like that?

#18 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-29 11:40:44

Quote

Supply Authority power factor can usually be between 0.6 and .9 lagging. A syncronous motor
can be run at a PF of 1.0. A sychronous motor can be used for PF correction.

Capacitors are normally used for PF correction eg, to improve an existing PF of 0.7 to perhaps
0.9.  O.95 is the economical limit.

In my experience you will not come across leading power factor in practice, it will be lagging as most loads are inductive not capacitive.

Agreed, the discussion of leading power factor arose from one of the first questions posed. My experience is that it is not a major issue in general, but the PDF document is an interesting read regardless.

( Some small generators do have problems with their waveform when used to supply electronic equipment and the manufacturers advice should be obtained.)

Edited by genset, 2009-10-29 11:41:18.


#19 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-29 11:54:19

View PostGary A, on 2009-10-29 11:33:44, said:

I was determined to have a generator to power everything except the hot water shower, (5,200 watt), and the air conditioner. I have a 30 HP diesel tractor with a PTO or an 11 HP diesel Kubota to drive a generator. I have since given up on the project. I already have a small gasoline powered generator. I have found that I can make the electric come back on by using the small generator.  :)  At least it seems that way. The outages are normally quite brief. By the time I run the extension cords and get the generator running, the power comes back on.

I have now decided that I want to use a battery backup system. Just like a computer UPS but much larger. It would normally use the main to stay charged but in case of a prolonged power failure, a generator could also be used to charge the batteries. Much more expensive but automatic switching is very convenient. A capacity of about 1400 watts for a couple of hours would be enough.

Genset, are you able to put together a system like that?

I dont have any experience designing and installing large battery back up systems I'm afraid, but most portable generators such as the IG2000 and KDE6700TA models feature a DC output which may be of use to you.


#20 Naam

Naam

    Star Member

  • Advanced Members
  • PipPipPipPipPipPipPipPip
  • 18,093 posts

Posted 2009-10-29 18:30:20

naam: my question is specific for my home which has 19 powerhungry aircons distributed evenly over three phases (only a third of them are running normally). are there no three-phase gensets in the range 15-25Kva available?

genset: 19 aircons... ok... doesnt the hotel you live in have a decent generator already...? Only kidding...there are indeed three phase gensets availabe in the 15-25kva range, but they are more costly as they are heavier duty, slow running (1500rpmk) gensets in the same range as the KDE16SS, the KDE20SS3 is one such model. Once you have determined your load requirement (remember to use starting wattage for your aircons in your calcuation), drop me a line and I will refer you to a specific size and model suitabe for your needs.

the starting amps of the aircon compressors are indeed a problem. if taken fully into consideration i would have to select overkill kVa capacity. a solution would be to switch off all aircons with the individual brakers, start the generator and then switch on the aircons one by one. slightly tedious but effective.

something similar applies to the obvious much more expensive three-phase sets. wiring the essential consumers including aircons seems to be a simple and extremely cheap solution as in my case each aircon is on a proprietory circuit with an individual breaker.

my load calculation (for a rather comfortable solution) including a safety factor of 20% shows a total of 14 kilowatts, that means 20 kVa should suffice. the "el cheapo" alternative but still feasible solution including a 20% additional factor is ~10 kilowatts and perhaps a 15 kVa unit.

your opinion please Genset.

#21 Naam

Naam

    Star Member

  • Advanced Members
  • PipPipPipPipPipPipPipPip
  • 18,093 posts

Posted 2009-10-29 18:45:29

View PostGary A, on 2009-10-29 11:33:44, said:

I was determined to have a generator to power everything except the hot water shower, (5,200 watt), and the air conditioner. I have a 30 HP diesel tractor with a PTO or an 11 HP diesel Kubota to drive a generator. I have since given up on the project. I already have a small gasoline powered generator. I have found that I can make the electric come back on by using the small generator.  :D  At least it seems that way. The outages are normally quite brief. By the time I run the extension cords and get the generator running, the power comes back on.

I have now decided that I want to use a battery backup system. Just like a computer UPS but much larger. It would normally use the main to stay charged but in case of a prolonged power failure, a generator could also be used to charge the batteries. Much more expensive but automatic switching is very convenient. A capacity of about 1400 watts for a couple of hours would be enough.

Genset, are you able to put together a system like that?
that's an easy one Gary. i have installed three systems each for continuous output of ~1,500 watts. got the inverters from India (cost each 225 US-dollars) and bought the batteries locally (two per system each 160Ah @ 4,300 Baht). the inverters switch automatically in milliseconds (computers and lights don't wink an eye) and of course have a built-in electronic charger. wiring inverter to batteries is childs play and done in a few minutes. a bigger problem is to connect the output to the locations you want if you own the average thai house with only half a dozen breakers  :)

#22 Gary A

Gary A

    Titanium Member

  • Advanced Members
  • PipPipPipPipPipPipPip
  • 8,974 posts

Posted 2009-10-29 19:17:33

View PostNaam, on 2009-10-29 18:45:29, said:

View PostGary A, on 2009-10-29 11:33:44, said:

I was determined to have a generator to power everything except the hot water shower, (5,200 watt), and the air conditioner. I have a 30 HP diesel tractor with a PTO or an 11 HP diesel Kubota to drive a generator. I have since given up on the project. I already have a small gasoline powered generator. I have found that I can make the electric come back on by using the small generator.  :D  At least it seems that way. The outages are normally quite brief. By the time I run the extension cords and get the generator running, the power comes back on.

I have now decided that I want to use a battery backup system. Just like a computer UPS but much larger. It would normally use the main to stay charged but in case of a prolonged power failure, a generator could also be used to charge the batteries. Much more expensive but automatic switching is very convenient. A capacity of about 1400 watts for a couple of hours would be enough.

Genset, are you able to put together a system like that?
that's an easy one Gary. i have installed three systems each for continuous output of ~1,500 watts. got the inverters from India (cost each 225 US-dollars) and bought the batteries locally (two per system each 160Ah @ 4,300 Baht). the inverters switch automatically in milliseconds (computers and lights don't wink an eye) and of course have a built-in electronic charger. wiring inverter to batteries is childs play and done in a few minutes. a bigger problem is to connect the output to the locations you want if you own the average thai house with only half a dozen breakers  :)

I think I would wire two 10 amp breakers into the battery system permanently. The other breakers would simply go dead when the mains power fails. My wife is one of those Thais who thinks unplugging the small kitchen appliances saves power. She would know that when we are on battery power to leave them unplugged. If I had a couple of fans, a refrigerator, my computer and the lights, that would do fine.

#23 elkangorito

elkangorito

    Licensed professional Cynic and 'Boundary Pusher'.

  • Banned
  • PipPipPipPipPipPip
  • 3,662 posts

Posted 2009-10-29 23:22:04

View PostNaam, on 2009-10-29 18:30:20, said:

the starting amps of the aircon compressors are indeed a problem. if taken fully into consideration i would have to select overkill kVa capacity. a solution would be to switch off all aircons with the individual brakers, start the generator and then switch on the aircons one by one. slightly tedious but effective.

something similar applies to the obvious much more expensive three-phase sets. wiring the essential consumers including aircons seems to be a simple and extremely cheap solution as in my case each aircon is on a proprietory circuit with an individual breaker.

my load calculation (for a rather comfortable solution) including a safety factor of 20% shows a total of 14 kilowatts, that means 20 kVa should suffice. the "el cheapo" alternative but still feasible solution including a 20% additional factor is ~10 kilowatts and perhaps a 15 kVa unit.

your opinion please Genset.

Doc. I've seen your installation & from memory, you have 3 or 4 switchboards grouped together.
This is not a good way to do things. I hate to tell you but you should have had only 1 switchboard from the beginning...and yes, it will be bloody big!
If you did have a "correct" installation (one switchboard), you may be able to easily fit "load shedding" contactors. What I'm trying to say is that if you had 1 switchboard for your circuit breakers, a "load shedding" panel (complete with phase failure equipment) would be an easy addition to your system. The only thing you would need to consider is if you want a "manual transfer switch" or an "automatic transfer switch". In any case, the transfer switch panel could be made to also accommodate the load shedding contactors.

#24 genset

genset

    Senior Member

  • Sponsors
  • PipPipPipPip
  • 130 posts

Posted 2009-10-30 04:41:39

View PostNaam, on 2009-10-29 18:30:20, said:



the starting amps of the aircon compressors are indeed a problem. if taken fully into consideration i would have to select overkill kVa capacity. a solution would be to switch off all aircons with the individual brakers, start the generator and then switch on the aircons one by one. slightly tedious but effective.


If you normally run all of your air conditioning  units all of the time, I would stick with a load calculation based on  the starting wattage of each individual a/c unit plus all your other  electrical appliances. Your 'tedious but effective' suggestion of  isolating each a/c circuit prior to generator startup and then turning  them on one by one, may work initially; but the random on/off cycle of  the a/c compressors as each room warms/cools/warms at a variable rate, may lead to a  situation a few hours (or more) later where the cycles sync once more, the  combined power requirement as the majority of your a/c compressors  start simultaneously, on an undersized generator, will trip the  generator breaker (overcurrent) or stall the set.

something similar applies to the obvious much more expensive three-phase sets. wiring the essential consumers including aircons seems to be a simple and extremely cheap solution as in my case each aircon is on a proprietory circuit with an individual breaker.

my load calculation (for a rather comfortable solution) including a safety factor of 20% shows a total of 14 kilowatts, that means 20 kVa should suffice. the "el cheapo" alternative but still feasible solution including a 20% additional factor is ~10 kilowatts and perhaps a 15 kVa unit.

If your total load requirement is 14Kw. Then 14Kw = 80% of 17.5Kw (22Kva rounded up) so a 22Kva generator would be the optimum size... It doesnt appear however, that your 14Kw load requirement was calculated using the starting wattage for all of your a/c units; if the 14Kw load was for your 19 a/c units alone (not including your other electrical appliances), it would mean an average starting wattage of just over 700watts per unit... this can't be correct, can it...?

your opinion please Genset.

Edited by genset, 2009-10-30 05:06:50.


#25 david96

david96

    Super Member

  • Banned
  • PipPipPipPipPip
  • 1,336 posts

Posted 2009-10-30 06:19:37

Here is the website with information on UPS systems available in Thailand. Follow the links.
Single and Three phase units.

http://www.chloridep...cts--Solutions/



 