Water Heater Questions, Important To Connect A Water Heater Electric System To Ground ?Electric cable going to the water heater must be big (thick) or any ?


44 replies to this topic

#26 david96

    Super Member

  • Banned
  • PipPipPipPipPip
  • 1,336 posts

Posted 2009-11-11 08:57:57

RCD/RCBO 10ma Class 1 40 msecs trip max.
RCD/RCBO 30ma Class 2 300 msecs trip max.

Class 1 used in higher risk areas, such as dental surgeries and wet areas.(AS3003)

Standing leakage current should not exceed 30% of the rating of the protective device.
Under a sensitivity test they must trip between 50% and 100% of the rating of the device.
The actual test is at 100% of the rating of the device in ma to earth. There is also a test button on the units that will stimulate an out of balance current to check the operation of the device.

In practice most RCD/RCBOs will trip at about 70% of their rating in ma. at an average time
of 20 to 30msecs.

An RCD has no overload or short circuit rating and must be have a protective device, HRC fuse or MCB on the line side of the RCD.

An RCBO has overload and shortcircuit protection it is a combination MCB/RCD.

An RCD or RCD/RCBO will not prevent you receiving an electric shock but it will minimise the risk of death or severe injury by indirect contact as the victim is disconnected from the source of supply within milliseconds.

Electric shock can cause cardiac failure.

The Safe-T-Cut units available in Thailand are generally RCBOs but they may not comply with
IEC or AS/NZ Standards.

#27 frenchFARANGbkk

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,049 posts

Posted 2009-11-19 15:45:57

Anybody can install RCBO in Bangkok ?

Thanks.

#28 Gulfstream

    Advanced Member

  • Members
  • PipPipPip
  • 47 posts

Posted 2009-11-19 22:04:19

Would an RCD/RCBO/ELCB Breaker in the Electric Service Box (Breaker Panel) work just as well as a Safety-T-Cut separate device?

Now having a condo upgraded with new Electric Service and cannot Earth for numerous reasons. Need protection for water heaters (as does OP), washer, and hob.

Planning to us an ABB brand in panel safety breaker. Any advice for or against this plan?

#29 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-20 05:44:54

View PostGulfstream, on 2009-11-19 22:04:19, said:

Would an RCD/RCBO/ELCB Breaker in the Electric Service Box (Breaker Panel) work just as well as a Safety-T-Cut separate device?

Now having a condo upgraded with new Electric Service and cannot Earth for numerous reasons. Need protection for water heaters (as does OP), washer, and hob.

Planning to us an ABB brand in panel safety breaker. Any advice for or against this plan?

That would be an even better solution than using the Safe T Cut, which by the way is a product I am not too impressive with. ABB has a hugh range of RCBOs for different applications and with different characteristics.

Their AC-types provides protection against overload and short-circuit currents; protection against the effects of sinusoidal
alternating earth fault currents; protection against indirect contacts and additional protection against direct contacts (I delta n=30 mA), while the A-types protection against overload and short-circuit currents; protection against the effects of sinusoidal alternating and direct pulsating earth fault currents; protection against indirect contacts and additional protection against direct contacts (I delta n=30 mA). However, the A-types for residential applications are not stocked in Thailand and ABB have recommended me to go for the AC-type.

Also, with regards to the different characteristics of operation ABB Thailand only recommend the C-characteristics to be used here. This should help you limit your search as the ABB pro M compact catalogue is almost 700 pages.

The below unit is the one ABB have recommended for my house that is under construction. ABB's distributor in Thailand is PMK Corporation Ltd. in Nonthaburi and their telephone number is 02 903 9999; e-mail: pmkgroupe@pmk.co.th

DS 951 AC type, C characteristic

In A Type code Order code EAN kg pc.
6 DS 951 AC-C6/0.03 16021351 413509 0.200 5
10 DS 951 AC-C10/0.03 16021369 413608 0.200 5
16 DS 951 AC-C16/0.03 16021377 413707 0.200 5
20 DS 951 AC-C20/0.03 16021385 413806 0.200 5
25 DS 951 AC-C25/0.03 16021393 413905 0.200 5

The DS9... series are 2-pole RCBO for 1L + N.

ABB pro M Compact catalogue can be downloaded here:

http://www.abb.com/AbbLibrary/DownloadCent...KMTdWVmHkmEigUH

Switch off auto proxy in your web browser before downloading as this catalogue is very difficult to download. It took me more than 10 tries before I succeeded.

Good luck

#30 Gulfstream

    Advanced Member

  • Members
  • PipPipPip
  • 47 posts

Posted 2009-11-20 21:01:30

View Poststgrhe, on 2009-11-20 05:44:54, said:

View PostGulfstream, on 2009-11-19 22:04:19, said:

Would an RCD/RCBO/ELCB Breaker in the Electric Service Box (Breaker Panel) work just as well as a Safety-T-Cut separate device?

Now having a condo upgraded with new Electric Service and cannot Earth for numerous reasons. Need protection for water heaters (as does OP), washer, and hob.

Planning to us an ABB brand in panel safety breaker. Any advice for or against this plan?

That would be an even better solution than using the Safe T Cut, which by the way is a product I am not too impressive with. ABB has a hugh range of RCBOs for different applications and with different characteristics.

Their AC-types provides protection against overload and short-circuit currents; protection against the effects of sinusoidal
alternating earth fault currents; protection against indirect contacts and additional protection against direct contacts (I delta n=30 mA), while the A-types protection against overload and short-circuit currents; protection against the effects of sinusoidal alternating and direct pulsating earth fault currents; protection against indirect contacts and additional protection against direct contacts (I delta n=30 mA). However, the A-types for residential applications are not stocked in Thailand and ABB have recommended me to go for the AC-type.

Also, with regards to the different characteristics of operation ABB Thailand only recommend the C-characteristics to be used here. This should help you limit your search as the ABB pro M compact catalogue is almost 700 pages.

The below unit is the one ABB have recommended for my house that is under construction. ABB's distributor in Thailand is PMK Corporation Ltd. in Nonthaburi and their telephone number is 02 903 9999; e-mail: pmkgroupe@pmk.co.th

DS 951 AC type, C characteristic

In A Type code Order code EAN kg pc.
6 DS 951 AC-C6/0.03 16021351 413509 0.200 5
10 DS 951 AC-C10/0.03 16021369 413608 0.200 5
16 DS 951 AC-C16/0.03 16021377 413707 0.200 5
20 DS 951 AC-C20/0.03 16021385 413806 0.200 5
25 DS 951 AC-C25/0.03 16021393 413905 0.200 5

The DS9... series are 2-pole RCBO for 1L + N.

ABB pro M Compact catalogue can be downloaded here:

http://www.abb.com/AbbLibrary/DownloadCent...KMTdWVmHkmEigUH

Switch off auto proxy in your web browser before downloading as this catalogue is very difficult to download. It took me more than 10 tries before I succeeded.

Good luck

Thanks Stgrhe, good info and bought 2 of the ABB safety's today, only one type was sold and has 30mA sensitivity. The shop confirmed
your suggestions are quite correct.

#31 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-21 07:42:54

You are welcome! Which type did you buy?

#32 frenchFARANGbkk

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,049 posts

Posted 2009-11-24 22:04:15

Gi,


Can you confirm that it's not useful to install a breaker in the bathroom as the sale person adviced when you already have a breaker in the consumer unit (box with many switches inside to cut electricity at different place of the condo). (one of this switch already cut electricity at every plug in the bathroom and also at the previous water heater).

I don't mind to pay 400 thb more to install the water heater but the kind of breaker box they want to add (just a switch ?) is quite ugly !

Thanks again.

#33 lopburi3

    Star Member

  • Global Moderators
  • PipPipPipPipPipPipPipPip
  • 39,756 posts

Posted 2009-11-25 10:35:23

Any breaker should be outside the bathroom - there should be a breaker/rcd built into the shower unit itself. Then the panel breaker. But make sure there is a ground - if in any doubt install another RCD outside bathroom. You are in a very bad position taking a shower if something goes wrong.

#34 Gulfstream

    Advanced Member

  • Members
  • PipPipPip
  • 47 posts

Posted 2009-11-29 18:35:10

View Poststgrhe, on 2009-11-21 07:42:54, said:

You are welcome! Which type did you buy?
Sorry for the delayed reply, bought the ABB RCD and will have it all installed shortly.

Why are so many posts advising to ground; I thought the RCD breaker would cut off in the event of a problem? Why RCD + Ground?

#35 elkangorito

    Licensed professional Cynic and 'Boundary Pusher'.

  • Banned
  • PipPipPipPipPipPip
  • 3,662 posts

Posted 2009-11-29 19:07:35

RCD protection is considered to be "Secondary" protection. "Primary" protection is earthing.

RCD's are electronic devices, which can fail. This is why they MUST be tested monthly by pressing the "test" button.
Conversely, a hard wired earthing system is less likely to suffer damage from surges in the electrical supply etc. As such, it will provide more reliable protection.

On a further note, there is not just one type of RCD...there are about four types. See the attached picture.

Attached File  types_of_rcd.gif   32.96K   13 downloads

#36 David006

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,060 posts

Posted 2009-11-30 08:03:18

View PostCrossy, on 2009-11-10 09:14:33, said:

View PostDavid006, on 2009-11-10 07:52:03, said:

Thanks for that...interesting... wonder what the logic/safety aspect the design is based upon...
I was repairing our cheapie Panasonic Plastic dual tub washer (only has a two flat prong plug) and noticed both motors have ground bonding connected which go no place....same with our the fridges...ah well!

Not being experienced in HT distribution AC theory....anyone know what the resistance to ground of the "neutral" standard is? I suppose theoretically it should be the same as local ground since it is effectively that at the source. Also I noticed there is always a few ac volts to "ground" on the neutral ...ie a pd.( I have seen this in several locations in Thailand)! Suspect this is induced voltage only..the source of ground hum..?
The Schuko is a very safe design, the outlets are shuttered and the plug fits into a recess, it is impossible to contact live metalwork whilst inserting/removing the plug from the correct outlet, in both versions the ground connects first / disconnects last. As to why we get these on Thai appliances, who knows.

The neutral-ground connection at the transformer should be a few ohms if it has a proper earth mat. Your local ground spike will likely have a few hundred ohms, which is why an RCD is necessary, a L-E fault will not pull enough current to drop the MCB.

The N-E potential you're seeing is the volt drop along the neutral under load, the ground is at the same potential as the neutral at the transformer.


thanks for that mate...I have installed parallel ground rods and would hope that the ground should also be nearer the neutral . I which were have seen "paralleled" ie multiple rods in electrical room grounds in Canada which produced an effective ground resistance of less than 3 ohms.

Interesting story re grounds...I was managing the installation of an early electronic telephone exchange which kept getting a corrupted database every summer . turned out it was the system/building ground which had been driven into the land fill on which the building was placed. On the recommendation of one of our power engineers who had "meggered" the ground for me... had to get a drilling rig in to sink and drive 100m long copper clad carbon filled rod!! Ground dried out every summer...

#37 lopburi3

    Star Member

  • Global Moderators
  • PipPipPipPipPipPipPipPip
  • 39,756 posts

Posted 2009-11-30 09:39:30

View PostGulfstream, on 2009-11-29 18:35:10, said:

View Poststgrhe, on 2009-11-21 07:42:54, said:

You are welcome! Which type did you buy?
Sorry for the delayed reply, bought the ABB RCD and will have it all installed shortly.

Why are so many posts advising to ground; I thought the RCD breaker would cut off in the event of a problem? Why RCD + Ground?
One thing the RCD will not prevent is a hot to neutral fault - that will require the overload breaker to trip. Not good if your left index is on neutral and right on hot.

In your water heater the ground wire will trip the breaker if the chassis/metal tank becomes hot. Without it you would be the ground and if the RCB failed could lose your life.

Have both. Please.

#38 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-30 15:41:43

View Postlopburi3, on 2009-11-30 09:39:30, said:

View PostGulfstream, on 2009-11-29 18:35:10, said:

View Poststgrhe, on 2009-11-21 07:42:54, said:

You are welcome! Which type did you buy?
Sorry for the delayed reply, bought the ABB RCD and will have it all installed shortly.

Why are so many posts advising to ground; I thought the RCD breaker would cut off in the event of a problem? Why RCD + Ground?
One thing the RCD will not prevent is a hot to neutral fault - that will require the overload breaker to trip. Not good if your left index is on neutral and right on hot.

In your water heater the ground wire will trip the breaker if the chassis/metal tank becomes hot. Without it you would be the ground and if the RCB failed could lose your life.

Have both. Please.

Isn't that one of the reasons why one should chose a RCBO before a RCD?

#39 lopburi3

    Star Member

  • Global Moderators
  • PipPipPipPipPipPipPipPip
  • 39,756 posts

Posted 2009-11-30 16:33:14

RCBO says it is a RCD and a breaker combined but in home use I have never seen them not combined here regardless of what they are called (although I am not in that business). The RCD trips the breaker as does an overload. But you really should have overload breakers of lower ratings than the Safe-t-Cut and main panel RCBO 50-60 amps. In most overload situations the circuit 15 amp breaker trips long before the RCBO breaker would trip for overload.

#40 Gulfstream

    Advanced Member

  • Members
  • PipPipPip
  • 47 posts

Posted 2009-11-30 21:07:54

View Postlopburi3, on 2009-11-30 09:39:30, said:

View PostGulfstream, on 2009-11-29 18:35:10, said:

View Poststgrhe, on 2009-11-21 07:42:54, said:

You are welcome! Which type did you buy?
Sorry for the delayed reply, bought the ABB RCD and will have it all installed shortly.

Why are so many posts advising to ground; I thought the RCD breaker would cut off in the event of a problem? Why RCD + Ground?
One thing the RCD will not prevent is a hot to neutral fault - that will require the overload breaker to trip. Not good if your left index is on neutral and right on hot.

In your water heater the ground wire will trip the breaker if the chassis/metal tank becomes hot. Without it you would be the ground and if the RCB failed could lose your life.

Have both. Please.
Thanks all for the wise info, just ordered earthing/grounding. A major job but prefer safety.
I had always thought the RCD was so sensitive it would trip before I got "fried", looks like it's not the case.

#41 lopburi3

    Star Member

  • Global Moderators
  • PipPipPipPipPipPipPipPip
  • 39,756 posts

Posted 2009-12-01 09:17:41

It is not a matter of not being sensitive - when set properly they are. But they can fail and it is always best to prevent touching a hot chaises (which is what the ground will do - short to ground/chaises will trip the overload breaker before you have a chance to touch it).

#42 Gulfstream

    Advanced Member

  • Members
  • PipPipPip
  • 47 posts

Posted 2009-12-01 18:54:51

View Postlopburi3, on 2009-12-01 09:17:41, said:

It is not a matter of not being sensitive - when set properly they are. But they can fail and it is always best to prevent touching a hot chaises (which is what the ground will do - short to ground/chaises will trip the overload breaker before you have a chance to touch it).
Got it, and thanks again. Will have all grounded.

#43 Gary A

    Titanium Member

  • Advanced Members
  • PipPipPipPipPipPipPip
  • 8,709 posts

Posted 2009-12-01 19:10:31

My condo has no ground (earth) available. Most hot water showers have an ELB built in but some don't. Turbora is one that doesn't. I'd make sure that the unit you buy has the ELB.

#44 Thaifan2

    Super Member

  • Banned
  • PipPipPipPipPip
  • 1,681 posts

Posted 2010-06-05 19:58:44

View PostGary A, on 2009-12-01 19:10:31, said:

My condo has no ground (earth) available. Most hot water showers have an ELB built in but some don't. Turbora is one that doesn't. I'd make sure that the unit you buy has the ELB.


The model i just bought has a ELCB ( same as ELB ?) .Turbora model ,DZ-3500E

#45 ronz28

    Senior Member

  • Advanced Members
  • PipPipPipPip
  • 910 posts

Posted 2010-06-10 02:20:48

Getting it right is a common problem elsewhere too. There needs to be a plug-in LED device that anyone can use to quickly determine if the wiring is proper since some of it isn't in Thailand and elsewhere.

KBR recently Lost $24.1 Million Fee Over Green Beret’s Death due to this type of electrocution:

KBR Loses $24.1 Million Fee Over Green Beret’s Death (Update1) - Bloomberg.com



 