Maximum Demand Calculation For Hua Hin HouseHelp with estimation needed


72 replies to this topic

#1 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-23 20:54:50

I and my wife are building a house i Hua Hin and help with a Maximum Demand Calculation would be highly appreciated.

GENERAL
The main meter will be 30/100 and the supply 3 phase. All appliances will be single phase and no plans exist for future 3 phase equipment. The power outlets in the living room area will among others be used for a 50" LED TV, DVD, pre-amplifier, five channel power amplifier (5 x 200W) and an active sub-woofer (1kW). A 1kW movable vacuum cleaner exists too.

LOUNGE / DINING / HALL

18 Down-lights (12W Low Energy)

20 Indirect Lights (18W Fluorescent)

12 Power Outlets (DGPO)

1 Alarm System

3 Ceiling Fans

KITCHEN

4 Down-lights (12W Low Energy)

3 Ceiling Lights (12 W Low Energy)

4 Power Outlets (DGPO) [Toaster & Coffee Machine]

1 Fridge/Freezer (SGPO) 1,430W

1 Hood 290W

1 Hob 6,600W

1 Oven 3,600W

1 Microwave Oven (SGPO) 1,220W

1 Dish Washer (SGPO) 2,300W

1 Water Purifier (SGPO) 100W

MASTER BEDROOM

9 Down-lights (12W Low Energy)

10 Indirect Lights (18W Fluorescent)

8 Power Outlets (DGPO)

1 Ceiling Fan

MASTER BEDROOM - WALK-IN CLOSET

2 Down-lights (12W Low Energy)

1 Power Outlets (DGPO)

MASTER BEDROOM - BATH

2 Down-lights (12W Low Energy)

2 Power Outlets (DGPO)

1 Extraction Fan

OFFICE

10 Down-lights (12W Low Energy)

8 Indirect Lights (18W Fluorescent)

10 Power Outlets (DGPO)

1 Ceiling Fan

INDOOR STORE

2 Down-lights (12W Low Energy)

2 Power Outlets (DGPO)

SECOND BEDROOM

9 Down-lights (12W Low Energy)

8 Indirect Lights (18W Fluorescent)

8 Power Outlets (DGPO)

1 Ceiling Fan

SECOND BEDROOM - WALK-IN CLOSET

1 Down-lights (12W Low Energy)

1 Power Outlets (DGPO)


SECOND BEDROOM - BATH

2 Down-lights (12W Low Energy)

2 Power Outlets (DGPO)

1 Extraction Fan

GUEST TOILETTE / POWDER ROOM

2 Down-lights (12W Low Energy)

2 Power Outlets (DGPO)

1 Extraction Fan

MAIN HOUSE - OUTDOOR

6 Wall-Mounted Lights – Front (12W Low Energy)

4 Wall-Mounted Lights – Terrace (12W Low Energy)

1 Power Outlet (DGPO) – Front

2 Power Outlets (DGPO) – Terrace

4 Pond Lights

1 Pond Pump


AIR CONDITIONING UNITS

1 Air conditioning Lounge/Dining/Hall 52,000 BTU (Inverter)

1 Air conditioning Office 18,000 BTU (Inverter)

1 Air conditioning Master Bedroom 24,000 BTU (Inverter)

1 Air conditioning Second Bedroom 24,000 BTU (Inverter)

WATER BOILERS

1 Main Water Boiler (For Main House's Bathrooms) 150 litres 1,800W

1 Kitchen Water Boiler 30 litres 1,800W

OTHER OUTDOOR APPLIANCES

1 Electrically Operated Main Gate

7 Terrace Floor Lights (12W Low Energy)

3 Terrace Ceiling Fans

2 Swimming Pool Lights

8 Flood Lights engaged by Alarm System (100W)

GUEST HOUSE - INDOOR

8 Down-lights (12W Low Energy)

6 Indirect Lights (18W Fluorescent)

12 Power Outlets (DGPO)

1 Ceiling Fan

GUEST HOUSE - OUTDOOR

1 Wall-Mounted Light

1 Power Outlet (DGPO)

1 Air conditioning Unit 18,000 BTU (Inverter)

1 Water Boiler (30 litres) 1,800W

GUEST HOUSE - BATH

2 Down-lights (12W Low Energy)

2 Power Outlets (DGPO)

1 Extraction Fan

LAUNDRY ROOM

2 Down-lights (12W Low Energy)

2 Power Outlet (DGPO) (excluding WM & Dryer)

1 Washing Machine (SGPO) 2,300W

1 Dryer (SGPO) 2,100W

OUTDOOR STORE ROOM

2 Down-lights (12W Low Energy)

1 Power Outlet (DGPO)

CARPORT

5 Down-lights (12W Low Energy)

1 Power Outlet (DGPO)

PUMP ROOM - INDOOR

1 Fluorescent Light (18W Fluorescent)

1 Power Outlet (DGPO)

1 Main Water Pump 920W

1 Irrigation (Sprinkler) Water Pump 920W

1 Water Filter

POOL EQUIPMENT ROOM - INDOOR

1 Fluorescent Light (18W Fluorescent)

1 Power Outlet (DGPO)

1 Swimming Pool Pump 1,000W

1 Swimming Pool Hydroxinator (MagnaPool Generator) 400W

PUMP ROOMS - OUTDOOR

1 Wall-Mounted Light (12W Low Energy)

1 Power Outlet (DGPO)

#2 tominchaam

    Senior Member

  • Members
  • PipPipPipPip
  • 198 posts

Posted 2009-11-23 21:04:19

As you and your wife are building the house what about asking her?

#3 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-23 21:12:08

View Posttominchaam, on 2009-11-23 21:04:19, said:

As you and your wife are building the house what about asking her?

I suppose the big boys have been bad to you today. Life must be really bad to you poor little man.

#4 Rimmer

    Banjo Picking Member

  • Global Moderators
  • PipPipPipPipPipPipPip
  • 8,213 posts

Posted 2009-11-24 14:09:27

How can a polite request for a power estimate go off the rails so quickly?

Pay no attention stgrhe I am sure Crossy will be along shortly.

#5 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-24 14:43:34

View PostRimmer, on 2009-11-24 14:09:27, said:

How can a polite request for a power estimate go off the rails so quickly?

Pay no attention stgrhe I am sure Crossy will be along shortly.

I really do not Rimmer and as a matter of fact I do not understand some of the blokes here. Thai Visa is a tremendously good forum with so many helpful and knowledgeable members, who sometimes go to extreme to help fellow members. Yet there are others who never contribute anything but only try to be funny on other member's expense. I suppose these guys are in complete disharmony with themselves and have such a strong need to show off so they can forget their miserable lives.

#6 elkangorito

    Licensed professional Cynic and 'Boundary Pusher'.

  • Banned
  • PipPipPipPipPipPip
  • 3,662 posts

Posted 2009-11-24 21:13:36

Hi stgrhe.

Your MD works out to be about 95 amps, which is close enough to be called 100 amps.

I should have the phase load balance completed by the end of this week.

#7 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-25 06:28:28

View Postelkangorito, on 2009-11-24 21:13:36, said:

Hi stgrhe.

Your MD works out to be about 95 amps, which is close enough to be called 100 amps.

I should have the phase load balance completed by the end of this week.

Thanks for your help mate. I shall be looking forward to see your recommendations.

#8 david96

    Super Member

  • Banned
  • PipPipPipPipPip
  • 1,336 posts

Posted 2009-11-25 07:08:13

You should contact the PEA and obtain their conditions of supply and if they can connect a
3 phase supply to your premises and if their distribution transformer can handle the extra load.

http://www.pea.co.th...p?name=FeeRates

#9 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-25 09:35:01

View Postdavid96, on 2009-11-25 07:08:13, said:

You should contact the PEA and obtain their conditions of supply and if they can connect a
3 phase supply to your premises and if their distribution transformer can handle the extra load.

http://www.pea.co.th...p?name=FeeRates

Thanks for the advice but it is already taken care of by the developer. The three phase line and a new transformer have been ordered and is due to be installed next month.

#10 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-25 09:38:05

View Poststgrhe, on 2009-11-25 06:28:28, said:

View Postelkangorito, on 2009-11-24 21:13:36, said:

Hi stgrhe.

Your MD works out to be about 95 amps, which is close enough to be called 100 amps.

I should have the phase load balance completed by the end of this week.

Thanks for your help mate. I shall be looking forward to see your recommendations.

I might have forgotten to mention that the circuits will be split types and not with a loop, like they were using for my house in Sydney back in the 80s.

#11 elkangorito

    Licensed professional Cynic and 'Boundary Pusher'.

  • Banned
  • PipPipPipPipPipPip
  • 3,662 posts

Posted 2009-11-25 17:14:09

A quick question stgrhe...you say "indirect lighting". What does this mean? Is it a light that is plugged into a GPO or something different?

#12 PeaceBlondie

    Star Member

  • Honorary Members
  • PipPipPipPipPipPipPipPip
  • 17,360 posts

Posted 2009-11-25 17:49:41

Let's give el kangorito a star rating.

#13 Crossy

    Bull Powered Member

  • Global Moderators
  • PipPipPipPipPipPipPipPip
  • 10,720 posts

Posted 2009-11-25 17:57:34

View Postelkangorito, on 2009-11-25 17:14:09, said:

A quick question stgrhe...you say "indirect lighting". What does this mean? Is it a light that is plugged into a GPO or something different?
Elk:-

http://www.schorsch....i_lighting.html

#14 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-25 19:34:44

View Postelkangorito, on 2009-11-25 17:14:09, said:

A quick question stgrhe...you say "indirect lighting". What does this mean? Is it a light that is plugged into a GPO or something different?

In some of the rooms the ceilings will be partly risen, squarish kind of boxes if you like, with hidden shelves which will be fitted with fluorescent light tubes. These light sources will give the applicable rooms indirect lights. Hence, some ceilings will fitted with two kinds of light sources of which the down-lights (direct light source) will be the other.

I hope this explains what I mean.

Edited. Sorry, elk, I forgot to answer your question whether these light sources are GPO or not and they are not as they are fixed installations.

Edited by stgrhe, 2009-11-25 19:37:32.


#15 elkangorito

    Licensed professional Cynic and 'Boundary Pusher'.

  • Banned
  • PipPipPipPipPipPip
  • 3,662 posts

Posted 2009-11-25 22:20:59

Thanks stgrhe. I asked because I wasn't sure of what your interpretation of "indirect lighting" was. I have met some people who seem to think it is other than that mentioned in the link Crossy posted e.g. a plug in bedside lamp.

#16 david96

    Super Member

  • Banned
  • PipPipPipPipPip
  • 1,336 posts

Posted 2009-11-26 05:52:47

View Postelkangorito, on 2009-11-25 22:20:59, said:

Thanks stgrhe. I asked because I wasn't sure of what your interpretation of "indirect lighting" was. I have met some people who seem to think it is other than that mentioned in the link Crossy posted e.g. a plug in bedside lamp.

Also known as pelmet lighting, the light source is not directly visible eg a 1 x36W batten flouor but one can not see the light directly.

#17 Tracer Round

    Senior Member

  • Members
  • PipPipPipPip
  • 185 posts

Posted 2009-11-27 20:00:22

"I suppose these guys are in complete disharmony with themselves and have such a strong need to show off so they can forget their miserable lives."

I'm sorry, but this comment really rankles. In every conversation with various people -- be it in a pub or club or online -- you will find those who throw out non sequitors or make off-the-cuff attempts (sometimes successful) at humor (however dry). Maybe he's taking a potshot at you, who knows?
The guy says to ask your wife...and you reply by saying he has a miserable life, has a need to show off and is in complete disharmony with himself (whatever that means, I'm not a psychologist).
Instead of blasting what you perceive as a heckler, you might try to grin and either ignore him, or use your craftiness to reply in such a way as to pass over him without trying to defame him.
Personally, I enjoy these oddball comments; they add spice and don't railroad the threads. Cut these guys some slack.

Conversation in a pub with several people around the bar:
A: "I need to find out the maximum demand for the electric system for the house I am building. Hopefully someone can do the assessment for free. Here is the list of all the lights and aircons and whatnot."
B: "Wow! A pond and a swimming pool and a guest house...what a mansion! That'll be some house. Maybe your wife knows someone locally who can figure out that demand thing for you."
A: "Excuse me, you poor little man. Did I ask for your show-off remarks? If you have nothing to contribute to actually helping me find out the maximum demand for the house then I suggest you take your miserable life and go spread disharmony elsewhere."


#18 elkangorito

    Licensed professional Cynic and 'Boundary Pusher'.

  • Banned
  • PipPipPipPipPipPip
  • 3,662 posts

Posted 2009-11-29 19:00:41

stgrhe, emails sent regarding Square D catalogs.

Your requirements are a little more than usually required & as such, may take me some time to complete.

For the purposes of updating this thread, your MD calc now stands at about 130 amps. As discussed, this is above & beyond the normal "domestic" limit but by limiting your maximum current, it can be brought down to 100 amps without detrimental effects. If you went ahead with a supply greater than 100 amps, CT's (current transformers) would be needed to "meter" your supply...a more expensive arrangement.

This week, I will identify the cicuit breaker arrangement for your Main Distribution Board (MDB). This will allow me to estimate the size DB (distribution board) you need. Also, the extra equipment you require will need to be in a seperate DB (mounted next to your MDB). Cutouts will be required in this extra DB to accommodate such things as a voltmeter & a selector switch.

I will be quoting Square D products since I have the basic catalog & price list. I propose using single pole RCBO's.

At the moment, it looks like your MDB will be at least 30 poles but I will give you the final result later this week.

#19 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-30 09:25:21

View Postelkangorito, on 2009-11-29 19:00:41, said:

stgrhe, emails sent regarding Square D catalogs.

Elk, thank you so much for the catalogs.

View Postelkangorito, on 2009-11-29 19:00:41, said:

For the purposes of updating this thread, your MD calc now stands at about 130 amps. As discussed, this is above & beyond the normal "domestic" limit but by limiting your maximum current, it can be brought down to 100 amps without detrimental effects. If you went ahead with a supply greater than 100 amps, CT's (current transformers) would be needed to "meter" your supply...a more expensive arrangement.

I appreciate what you are doing and am very grateful for your advice and support. I do understand the 'dilemma' with regards to the excess current and will thus cancel my first idea of using ABB Tmax circuit breaker with electronic limiting circuit and opt for a less sophisticated solution for the sake of reliability.

View Postelkangorito, on 2009-11-29 19:00:41, said:

This week, I will identify the cicuit breaker arrangement for your Main Distribution Board (MDB). This will allow me to estimate the size DB (distribution board) you need. Also, the extra equipment you require will need to be in a seperate DB (mounted next to your MDB). Cutouts will be required in this extra DB to accommodate such things as a voltmeter & a selector switch.

I shall await your suggestions with great interest.

With regards to the main circuit breaker I wonder whether it is a better idea to keep that unit in a separate box altogether and add HRF's? When looking at the Square D catalog it looks like there is no space for HRF's in their DB's and since the main power line will be under ground in PVC conduits I suppose one should add HRF's as the insulation is probably insufficient compared to Western standards.

View Postelkangorito, on 2009-11-29 19:00:41, said:

I will be quoting Square D products since I have the basic catalog & price list. I propose using single pole RCBO's.

Will a single pole RCBO really be as good as a 1L+N pole RCBO? I taught it would always be a better solution to cut-off both the live and the neutral and not just the live?

#20 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-30 15:54:58

To reduce the power consumption slightly I have agreed with the builder to delete the dedicated hot water boiler from the kitchen and instead connect the kitchen's hot water to the main hot water boiler. The will delete 1.8 kW from the power consumption.

#21 Naam

    Star Member

  • Advanced Members
  • PipPipPipPipPipPipPipPip
  • 16,834 posts

Posted 2009-11-30 17:05:50

View Poststgrhe, on 2009-11-30 15:54:58, said:

To reduce the power consumption slightly I have agreed with the builder to delete the dedicated hot water boiler from the kitchen and instead connect the kitchen's hot water to the main hot water boiler. The will delete 1.8 kW from the power consumption.
you are in good hands with ElKangorito BUT i doubt that the 52,000 btu unit is single phase and i strongly doubt that you need a 52k unit. please reconsider, plan smaller units instead, have a better airflow and save energy by using only the capacity you need.

#22 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-11-30 19:23:08

View PostNaam, on 2009-11-30 17:05:50, said:

you are in good hands with ElKangorito BUT i doubt that the 52,000 btu unit is single phase and i strongly doubt that you need a 52k unit. please reconsider, plan smaller units instead, have a better airflow and save energy by using only the capacity you need.

Yes, he is very good and indeed a true gentleman, I take of my hat and bow.

I know something is not right with the A/C and I have therefore asked another company to estimate the need in the applicable area. The 52,000 BTU figure was actually suggested by an engineer from Siam-Daikin in Bangkok after I had given him all relevant parameters and a layout of the house. Sadly he wouldn't reveal the formula he used. I am not a fully novice in this department but my knowledge is very dated and I simply do not remember how to carry out the calculation properly. My intuition tells me that something around 36,000 BTU or even less is probably more realistic.

I remember though that volume, insulation types (U-values), outdoor temperature and humidity, number of sunny hours per day, window sizes, glass thickness (single / double / triple), direction North / South etc. all matters but not their relation to one another.

#23 david96

    Super Member

  • Banned
  • PipPipPipPipPip
  • 1,336 posts

Posted 2009-12-01 06:46:30

Schneider Multi 9 C60/120 range. Square D is now Schneider.

Here is their website in Thailand.
http://www.schneider-electric.co.th/sites/...function_id=108

#24 stgrhe

    Super Member

  • Advanced Members
  • PipPipPipPipPip
  • 1,289 posts

Posted 2009-12-02 12:02:17

View Postdavid96, on 2009-12-01 06:46:30, said:

Schneider Multi 9 C60/120 range. Square D is now Schneider.

Here is their website in Thailand.
http://www.schneider-electric.co.th/sites/...function_id=108

Thanks David! Elkangorito has promised to chose a suitable circuit breaker for me so I will await his recommendations as there are so variables that I do not fully understand.

#25 katabeachbum

    Titanium Member

  • Honorary Members
  • PipPipPipPipPipPipPip
  • 9,725 posts

Posted 2009-12-02 12:25:01

View Poststgrhe, on 2009-12-02 13:02:17, said:

View Postdavid96, on 2009-12-01 06:46:30, said:

Schneider Multi 9 C60/120 range. Square D is now Schneider.

Here is their website in Thailand.
http://www.schneider-electric.co.th/sites/...function_id=108

Thanks David! Elkangorito has promised to chose a suitable circuit breaker for me so I will await his recommendations as there are so variables that I do not fully understand.

samsib/roy in 3 phase/4 wires is an extreme powersupply for a villa, and as listed your peak power will never be close to the limit. But if this is supplied to you, there is no need to choose smaller supply/meter. You could manage with 30/100 in onephase or 15/45 in 3phase/4wires.

For aircons I would choose several smaller units rather than few large ones. Better flow, and still have aircon if one fails for a couple of days.



 