electau, on 2012-02-22 06:53:16, said:
The main neutral is earthed to an electrode at the main switch board (MSB). If there is more than one distribution board (DB) in an electrical installation such as in a multi tenanted building (eg a condo) a separate earthing conductor must be run from the main switchboard earth bar to each distribution board. The DBs earthing must not be bonded to the neutral.
In practice in Thailand the earth conductors at the distribution board MAY be found bonded to the sub main neutral. It is possible that this MAY be permitted in Thailand if the distribution though the building are reticulated or rising sub-main(s) from the main switchboard. In other words the submain neutral becomes a PEN conductor, the same as the main neutral.
Nothing in the PEA document on that subject.
If you live in a condo you should have a L. N. and E into the distribution board (ie consumer unit).
Note. the SAFE-T-CUT adjustable sensitivity RCBOs have a 5mA setting. This 5mA is mentioned in the NEC for their GFCIs (RCDs).
It might be noteworthy to mention that GFCI's are usually at the receptacle (is the receptacle). ie: RCD circuit protection is not common in the states.
And, no issues here, but it's not clear to me where you are going with this thread? Like, are you doing research for a defacto Thai code, or?? Just curious.