If I may, I'd like to present an example of calculating generator size. If I have left anything out, I hope that Genset will correct me.
Again, this is merely an example.
Again, this is merely an example.
Thank you Elkangorito, your explanation of how to calculate the surge load for motors typically found in the home is a very useful addition to the thread. Historically, when L.R.A and F.R.A data-plate info is not available, I have multiplied the running watts by 3 where small motors of the type in your example are present, but I am happy to defer to your experience and electrical knowledge in using a multiple of 4 as you have suggested. As a rule of thumb, because most homes contain appliances with motors such as those listed in Elkangorito's example (and because L.R.A and F.R.A. may not be available on the motor data-plate), I will always post the Kw (alongside the Kva) rating of a machine, based on a power factor of 0.8, to enable accurate sizing and generator selection based on your load requirement.
Quote
"Home" generators typically have 2 ratings...a "continuous" rating & a "surge" rating. You may also notice that generators are sized in VA (Volt Amps) & usually not in kilowatts...there is a good reason for this. If you want to know the reason, feel free to ask.
When you're considering the purchase of a generator, the very least you should expect is good, accurate information to help you select a generator best suited for your needs, and not just some guy trying to move a boatload of cheap generators, who has little if any more knowledge about the product than you. The misapplication of an under sized generator is the most common problem I see out there and is normally the result of poor advice from the seller/distributor to a customer, an incorrect load calculation, or no load calculation at all.
Let's look at the ISO 8528-1:2005 ratings for generators and then discuss how each rating translates into home use.
There are four ratings; we are only interested in the first three with respect to 'home' use, they are;
ESP – Emergency Standby Power Rating
LRP – Limited Time Running Power (generally referred to as a Standby Rating)
PRP – Prime Power Rating
ESP – Emergency Standby Power Rating
Light duty, portable, single cylinder sets running at 3000rpm; rated to run for a maximum 200hrs a year (that's 3.8hrs a week) with a variable load at the alternators maximum load rating, no overload permitted.
LRP – Limited Time Running Power Rating ('Standby Rating')
Heavier duty, normally a permanent installation, multiple cylinder engines, running at 3000rpm or 1500rpm; rated to run for up to 500hrs a year (that's 9.6hrs a week maximum) with a constant load at the alternators maximum load rating, no overload permitted.
PRP – Prime Power Rating
Heavy Duty, permanent installation, multiple cylinder engines, running at 1500rpm; rated to run for an unlimited period of time with a variable load at the prime rating of the alternator; typically an overload of 10% in any 12 hour period is permitted.
To better understand why a particular rating is attributed to a generator for home use and more specifically, why it is important that LRP Standby Ratings should be limited to a maximum 500hrs operation a year and PRP Prime ratings are not, we need to look at aspects of the engine and alternator.
Voltage and Kva ratings of alternators are dictated by a number of factors; the length and size of the copper windings, the length of the lamination stack and the amount of cooling air passing through the alternator etc.
The class of insulation material used to protect the copper windings is a key factor. Resistance of the copper wire making up the alternator windings causes its temperature to rise as a current is passed through it… the more current, the more heat; the more heat, the shorter the life expectancy of the insulation material, with sufficient heat the insulation material will fail and the alternator will burn out.
NEMA (The National Electrical Manufacturers Association) recognizes four classes of insulation material for use in alternators (A, B, F and H). The difference between each class being the maximum temperature at which the copper windings can operate for each of two duty cycles; continuous use and standby use.
Continuous Use:
Running 24 hours a day, 7 days a week, the maximum operating temperature of the copper windings permitted by the NEMA insulation classes in degrees C are; Class A-100, Class B-120, Class F-145 and Class H-165.
Standby Use:
As standby use involves less running hours (that's the maximum 500hrs a year for standby use remember), the NEMA insulation classes allow the alternator windings to operate at up to 25 degrees C hotter; Class A-125, Class B-145, Class F-170 and Class H-190. The ability of the copper windings to operate up to 25 degrees C hotter for a limited period, allows the alternator to generate more power, hence the higher standby rating.
The maximum operating temperature of the copper windings is made up of two parts; the ambient environmental temperature and the temperature rise resulting from the operation of the alternator. If the ambient temperature is 40 degrees C, then deducting that figure from the maximum operating temperature for each class, gives us the temperature rise permitted for each class due to use.
A 1500rpm engine can be rated for use as a standby or prime mechanical power source, but a 3000rpm engine can only ever be used as a standby mechanical power source…these high revving engines are simply not designed to operate as a prime mechanical power source; this is concrete, regardless of what any dealer or distributor tries to tell you…
So…to simplify and summarize I will use the example of two Kipor generators, the KDE12STA and KDE16SS.
The KDE12STA is a 3000rpm, single phase generator. The alternator features class F insulation and the complete generator (engine and alternator combination) is rated as an LRP set for Standby Power use only. It should be operated at its maximum load rating for up to a maximum of 500hrs a year (9.6hrs a week maximum) and should give you good reliable service over the long term. However, as we have discussed, if you choose to operate this generator at or above its maximum load rating for a period exceeding the maximum runtime, you should fully expect to experience problems with the under rated mechanical power source (engine), or for the alternator insulation to fail and burn out at any time. It is a false economy to 'save' money by purchasing a standby generator only to then commit it to a prime power role. This is misapplication of the generator and you should fully expect to experience problems.
Note; if sufficiently rated, this same alternator driven by a 1500rpm machine could be used as a prime power source, as long as the heat in the copper windings does not exceed the class F temperature rise for continuous use. This is achieved by reducing the maximum output of the alternator from the maximum standby rating to the prime rating stamped on the alternator.
The KDE16SS is a 1500rpm, single phase generator. The alternator features class H insulation (the highest of the NEMA insulation classes) and the complete generator (engine and alternator combination) is rated for use as both a PRP set for Prime Power use and an LRP set for Standby Power use (13Kva/10.4Kw and 15.5Kva/12.4Kw respectively) according to application. The KDE16SS may be operated as a Prime Power source, at its Prime Power rating, continuously, for an unlimited period. However, as with the KDE12STA, if used as a secondary Standby Power source, it should be operated for up to a maximum 500hrs a year at its maximum Standby rating, operating this generator at or above its maximum load rating for a period exceeding the maximum runtime will eventually result in failure of the class H insulation and subsequent failure of the alternator.
Regardless of whether you are considering a generator for a Prime Power or Standby application, I would strongly recommend you follow my earlier suggestion that your generator be sized so that your maximum load requirement falls between 70 and 80% of the alternators rated output (70 to 80% of the Prime rating for Prime Power applications and/or 70 to 80% of the Standby rating for Standby Power applications). Among the benefits of sizing a generator in this way, are a reduction in the amount of fuel used, reduced strain on the engine, reduced thermal stress on the alternator insulation and a reduction in noise pollution; it also allows capacity for growth in your electrical needs.
My motivation for discussing this now, other than to offer advice to readers, is the result of a recent blizzard of emails between myself, the manufacturer and the distributor in Thailand, regarding the rating for the SS (ultra silent) range of Kipor machines. The manufacturer had initially represented their posted rating as being for Standby use (language and terminology issues), but I now have the accurate ratings sorted out and have amended my earlier posts to reflect the change.
I hope I haven't muddied the waters with this explanation; these are important points regarding generator sizing and selection, if you found it a little confusing please try giving it another read through.
Genset